GE RX3i Devicenet Drive stop for no reason

wilsonzhu

Member
Join Date
Jan 2008
Location
vancouver
Posts
278
HI, I have a project using GE RX3I, some drive occationaly stop for no reason, and operator are able to restart it, No error code, This has happened to may different drives- all within cabinet #2, rack2,3&4, Please help?
 
The answer is here.
.
.
.
.
.
.
.
Now, please give us details of your system and you may get better guesses as to the cause.
Maybe you need to move them all to Cabinet #7 (Cabinet of the Tiger!), it is my lucky cabinet.
 
Last edited:
Everything happens for a reason, even if it's not apparent to you.

The first few things I would want to know if I was troubleshooting this:

1. What DeviceNet scanner module are you using on the RX3i ?
2. What model of drives are these ?
3. What is the part number of the DeviceNet interface for the drives ?
4. How many drives are on the network ?
5. What other devices are on the network ?
6. How long has the network been installed ? Is this an ongoing problem or a recent development ?
7. Do the drives have a parameter that configures how the drive will react to a DeviceNet connection failure ?

Some additional information about the system under control would be nice; I have no idea what industry you are in and how your facility is configured, so the fact that these are in "cabinet #2" provides very little information to me other than the inference that the RX3i controller might not be in the same cabinet.
 

Similar Topics

We Sometimes face problems in Rx3i device-net module talking to a servo valve controller , How we can troubleshoot the communication issues ?
Replies
0
Views
1,467
Anyone have any experience getting a IC694DNM200 working with a IC695CPU310? Specifically getting the device net card to scan, currently the 'NET...
Replies
2
Views
1,799
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
Replies
14
Views
389
Hi, we are using Rx3i CRU320 redundant PLC system and we noticed a discrepancy between Primary and Secondary controller. Couple of variables (DI)...
Replies
8
Views
284
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
104
Back
Top Bottom