Hey All,

Have a little project in which I am metering Liquid Nitrogen in kg/hr. We only have the instantaneous flow rate available and the client would like to see the daily total.

System is an AB Control Logix.

Looking for very accurate data.

Thx,

K
 
Looking for very accurate data
How would you define VERY ACCURATE?
Does your flow meter have a totalizer?
If not What is your sample rate and what is your total scan time of the plc?
 
Very Accurate.....from client.....is +/- 1%

No totalizer on the meter.

Last Scan is at 27ms avg at 31ms.


We will use that totalizer pre-define data type tonight and will trend the instaneous over 24 hours compare and see if we are out to lunch or not.
 
There are various sources of error, and A-B does a good job noting the timing issues for totalizers.

I'd do a very careful read of the totalizer comments (more than just the one below) in this A-B publication:

http://literature.rockwellautomation.com/idc/groups/literature/documents/wp/logix-wp008_-en-p.pdf

iep9fr.jpg
 

Similar Topics

Dear Friends, Is there a special function block in S7-300 which can be used to have a total counter value , from a flow rate value? For...
Replies
12
Views
6,096
I have a fluid delivery system that controls flow in Pounds\Min. I need to convert that to GSM.(grams\meter sq.) Any math wizz's out there have a...
Replies
14
Views
4,475
I'm a real novice so please be kind. I have an Automation Direct DL-450 PLC. I plan on taking the pulse outputs from a flowmeter into the DC...
Replies
4
Views
4,715
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
199
Dear All, I need a sample PLC program to count the output pulse of a mass flow meter so that a specific amount of mass (for example 100gm)can be...
Replies
2
Views
173
Back
Top Bottom