Hello, all I am hooked from an idec PLC to PF 400 Drive and need to read and write data via modbus rtu over rs485 I got it all hooked up correctly but its been 2 years since I had a scadapack hooked to 3 of these drives and talking and cannot remember the addressing. PF 400 has Address (Decimal) 8192 for writing logic commands but what is that in modbus? Stupid question I know, but I dont remember how AB uses their parameters and how to read and write to an address like that. And now I am using a different type PLC.
 
When the PowerFlex 4-series user manuals refer to "Registers" they mean Modbus Holding Registers, which are commonly referred to as "40000x" registers because old Modicon controllers prefixed a "4" to the Holding Register memory.

So Register 8192 (decimal) is "48192" in Modicon addressing.

More specifically, you will use Function Code 0x06 (write Single Register) with offset 0x2000 (hex) = 8192 (decimal) to write to the 16-bit Command Word.

Appendix E of the PowerFlex 400 User Manual is the best reference to keep handy for this.
 
Yea ive been up and down the manual i was just wondering about their decimal addressing i guess 8192 = 48192 or 48193? since idec is offset buy one i believe.
 
Yeah, the 0 vs. 1 offset thing is a notorious issue in Modbus.

In the PowerFlex 4-series drives, "register 8192" is based on the first register having an offset of zero. 8192 decimal = 0x2000 hex, so if you looked at the Modbus data in a serial analyzer you would see "20 00" in the Offset field.

If you're dealing with a controller that considers an offset of zero to be "Modbus Register 40001", then the Command Word is "48193" and the Speed Reference word is "48194".
 

Similar Topics

how can i communicate with powerflex 400/40 through arduino with the help of modbus rtu/tcp. what is modbus register mapping of powerflex 400?
Replies
1
Views
1,711
Hello I am a newbie so apologies in advance if I am not making sense or miss important information. I am trying to setup a PID Loop on a...
Replies
1
Views
6,263
Hi All My issue is with an MSG error code 37 - 'Message timed out in local processor' between an ML1400 and 8 Powerflex 4M's. When the VSD's are...
Replies
14
Views
8,909
Evening all, Can someone please tell me (i know the manuals say it is possible), if MicroLogix 1400 PLC will communicate thru 1763-NC01 cable to a...
Replies
7
Views
8,550
Hello I have a powerflex 400 of 25HP for a 60amp 25HP motor, the motor have a belt that move the clarifier of milk. It is a process that requires...
Replies
11
Views
4,181
Back
Top Bottom