i have a PLC that its optocoupler barriers burn, in addition, PLC has a high current leakage. on the other hand, some of the indicators in HMI show a value different from related transmitter. does these problems relate to each other? please help me.
 
Burned opto isolation barrier and high leakage current in my book, would add up to the wrong voltage being applied to the card.

Now for us to be of any real assistance to you you need to tell us PLC brand, with model numbers, and also the Input and output card numbers.

The HMI brand and full model number may also help as well
 
at first, i must appreciate you for your quick answer. but i am confused because:
applied voltage to the card is the output of the optocoupler. therefore you mean applied voltage to the optocoupler is wrong. therefore i must measure the applied voltage to the optocoupler.
am i right?
 
This is why I asked for PLC part numbers

I was thinking the Opto was on the PLC input
but you now appear to be talking about a seperate module before the PLC input

Now it still stands that wrong voltage (High Voltage) or if DC maybe wrong polarity could burn up an Opto.

You may even help if you show us a diagram of what you have wired .
 

Similar Topics

Just looking at the manual for 1734-OW4 and it states its "4 type A Normally Open electromechanical relays" but right below it there is a spec for...
Replies
5
Views
2,552
I have an IFM Efector 1/4 turn valve limit switch (IN0177). Operating on 115VAC. Problem: The PLC input is energized with limit switch not...
Replies
14
Views
4,009
Hello all. I have a scenario where I am trying to operate a 120Volt coil relay from a transistor output photoeye. I am getting a voltage of 36 to...
Replies
17
Views
5,166
Installing a IR T/C onto a DeviceNet Flex IO drop. Card is a thermocouple card 1794-IT8/A. According to the manufacturer, I'm getting leakage...
Replies
0
Views
1,911
Hi There! A customer of us wants to add a earth leakage protection (max 400mA) device in de power supply of my control cabinet. This cabinet...
Replies
9
Views
9,288
Back
Top Bottom