Hi friend.....

I have a little problem with this cable....


This cable has a out dh485 with this i can setup ok.... but the other rs232 i can't see my plc by this port.... What need to do???

I hope yours comments friends....
 
It is not a true RS232... what PLC/CPU are you trying to communicate to ? you may need another cable
 
Hi friend....

I have a dell d830 with xp sp3 and plc slc500 5/04...I don't have the dh+ cable...

And this cable its usb thru rs232 or dh485..

With dh485 i do it setup.... But usb thru rs232 i can't make the auto configuration...

Thanks.....
 
peppin23joe;476357} said:
With dh485 i do it setup.... But usb thru rs232 i can't make the auto configuration...

The DB9 connector on the bottom of this device is not for RS232 connections. It for connecting to DH485 devices that have a DB9-style connector.

If you are trying to use regular RS232 communications, you will need to buy a USB to Serial port adapter. Luckly, they are alot less expensive than your 1747-UIC.
 
Your 1747-UIC will only work if the serial port on your SLC5/04 is configured for DH485 protocol.

The serial port on your SLC5/04 can be configured for DF1 (it's default configuration),
DH485, ASCII, or Modbus (if it's a newer unit). If you have the offline file for it then check
it's channel configuration. If you can post the .RSS file (zip it first) then someone here will help you look.

If the port is configured for DF1 and your PC does not have a real serial port then you will need a USB to serial adapter. Go back to your other thread and look at the info about the "Keyspan" adapter.
 

Similar Topics

I'm attempting to go online to a Micrologix 1500 using a p.c. without a serial port. The 1747-UIC USB to RS232 interface won't let me on. RS Linx...
Replies
4
Views
5,906
I don't know if it is available yet, but I found the manual on-line. http://www.ab.com/manuals/cp/1747-in063a-en-p.pdf Tell the IT guy that gets...
Replies
0
Views
2,210
Hi all, I have a SLC 5/02 that's been gathering dust for the past couple years that I want to have some fun with. The only problem is I don't...
Replies
9
Views
3,898
Hi All, I have SLC 5/04 which is already running plant. Now i want upload load the program from that PLC. i have connected RS232 cable and check...
Replies
9
Views
3,736
What is a good USB to DH485 programming cable that someone could recommend? I would need it to work in VMware running XP Pro SP3. What about...
Replies
16
Views
7,305
Back
Top Bottom