How do I connect a Rosemount 3051T Pressure Transmitter to a Modicon Micro 612-03 PLC

ShaunH

Member
Join Date
Feb 2012
Location
Norwich
Posts
5
Hello, I am entering the final stages of the PLC program using a Modicon Micro 612-03 I used a loop calibrator (4-20mA) to simulate the pressure transmitter before connecting it up to see if the program is working correctly.

Once I proved that the program was working correctly I connected the pressure transmitter up by providing an external power supply (24v) and also connected the loop which goes to the PLC to the device as well.

when i operated the system I was getting 4095 on the analog input which I believe to be full scale, which is not what it should be.

Im not entirely sure about the wiring which I have done I have been told that there needs to be a resistor put in the loop to control the input loop current at 4-20mA. But from looking at the PLC where the analog connects to internally there is a 250 ohm resistor??

Please help o_O
 
If you didn't need a resistor for the current simulator (loop calibrator), you don't need one for the real thing. Yes, a resistor is needed on an analog input, but the resistor is likely built into the analog input in your case.

You need to review how you wired the power supply in the loop with the transmitter and the analog input

34iimj4.jpg


Pay no attention to the colors, but pay particular attention to the polarity of the connections. Your PLC is the 'instrument'. The Rosemount is the xmtr.
 
Ah okay ill give that a go, then would i take two seprate wires for the loop to the analog input. or are the connections to the plc the analog inputs?
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
39
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
87
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
104
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
335
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
Replies
5
Views
288
Back
Top Bottom