I am having trouble with an SQI step not advancing. Was wondering what would cause this to happen. The value in the Array relative to the control position matches the value in the source array. The rung with the SQI and SQO instruction is true...it just seems to stop there. It was my understanding that when the source array value matches up with the SQI array value, thats what triggered it to advance to the next step. I am using a compact logix L32E.
Thanks for any help.
 
If it's like the PLC-5, then the SQI must make a false to true transition. This is one of the reasons I don't use the built in SQI/SQO instructions. At one time, I thought I fixed the problem (in a PLC-5) by using a oneshot, but that doesn't work when the sequencer enters a step in which all the inputs are already true.
 
Your trigger input probably reaches a point where it is true (ON or = 1) and stays true on every PLC scan. Therfore your SQI will not advance if it does not see a false-to-true transition.

It is always risky to use the data inside the SQI or SQO as the triggering input. If you insist on using the dog to chase its own tail, then it should be combined in series with something else that goes on/off regularly, such as a bit from a counter or timer.
 
Great, glad to hear about your success. Would you post your SQI and SQO rungs to show how you solved the problem?
 

Similar Topics

Hi folks I'm currently upgrading a control system that's nearly 20 years old from a 1756-L61 last programmed using version 20 logix5000 to a...
Replies
1
Views
1,334
Hi All, I need some clarification on sequencers, I researched this forum but haven't been able to find a good explanation, including the ones...
Replies
10
Views
5,067
hi guys, I have been task with modifying a machine. We are taking out some cameras and putting in photoeyes for part present sensors. There are...
Replies
9
Views
2,988
Friends, anyone can help me to understand the meaning of MASK in SQI instruction. IF someone has any example in ladder logic that would be...
Replies
2
Views
1,445
I am a student at LWIT in Kirkland washington and am trying to work on a couple labs for my PLC class. I have the pdf's from Allen Bradley and...
Replies
3
Views
6,886
Back
Top Bottom