The trip class is an I^2t curve between the pick-up point, usually 115-125% of the Set current (the Simocode is 115%), below which it never trips and 600% of the Set current, then a time value at the 600% level. So Class 10 = 10 sec, Class 20 = 20 sec, Class 30 = 30 sec etc.
If you have a motor with a FLC of 80A and you set the Class 10 OL trip level to 60A, it would trip at 360A in 10 seconds, but at 70A it will also eventually trip, even though your motor is not fully loaded. So that would be a waste of motor, you may well have just used a smaller one.
If you want a trip level based on current that is NOT associated with the OL protection curve, let's say for mechanical jam detection/protection, then use the Over CURRENT trip protection function, not the over LOAD. That function is a simple upper limit, with or without a time delay, and ignores everything below that.