I'd like to ask what is the best to communicate method between CompactLogix (1769-L31) & Siemens S7-1200 1214-CPU?

There are space to add in additional module in the panel. The distance is about 60 meters from each other. Non high speed require.

Thank you.:site:
 
Also look at **** gateways, I've used these to connect ControlLogix to S7-300. They work by connecting to the PLC's and a little bit of simple script to transfer the data
 
I would go the modbus tcp route
It's probably built in to ab, I know it is with Siemens 1200
 
There are several different ways to do this.

I would not use Profibus unless you need high speed; it is both costly and complex to configure on the CompactLogix side.

Since the S7-1200 supports Modbus/TCP, I would recommend a gateway device that supports both Modbus/TCP and Allen-Bradley DF1.

The Digi One IAP and HMS Communicator, as well as the Red Lion DataStation Plus are the first few that come to mind.
 

Similar Topics

I am new to Siemens and we have to convert a CompactLogix program over to a S7-1200 PLC. We are having a hard time finding a comparable...
Replies
17
Views
4,207
Hello again, I am currently attempting to retrieve one integer file from an existing MicroLogix 1200 that I have added a NET-ENI to...
Replies
37
Views
10,520
Hi, I've got a problem in communicating those 2 plcs. I need data exchange between them. I'm not familiar with AB so I cannot provide accurate...
Replies
2
Views
2,633
Hello, I have a panelview plus that reads from 4 different PLC's. 2 of these used to be Micrologix PLC's and someone else went and updated them to...
Replies
3
Views
95
Hi All, I'm just trying to understand the reason behind something I recently experienced. Background: The system contains 4 CompactLogix...
Replies
2
Views
151
Back
Top Bottom