Control Logix IO Configuration Change Online

Stuntman

Member
Join Date
Mar 2012
Location
Arkansas
Posts
33
I have a control logix PLC that is controlling a few power flex 70's via a 20-comm e module(ethernet/IP). I need to migrate the VFD's to a separate 1756-ENBT module and change the IP addresses of the power flex 20-comm e modules

Is it possible to change the IP address of the 20-comm-e module in the IO configuration tree of RSLogix 5000 while online without halting the PLC processor. I am guessing yes but its been a while and I cannot remember.

My plan is to modify the IP of the drive using the HIM then modify just the IP address in the IO configuration tree while online.
 
I am afraid you will not be able to accomplish this the way you've envisioned it.
After editing the 20-COMM-Es addressing via the HIMs you will have to reflect the changes within the RSL5K Offline application file modules' configuration applet and then download the edited file to the CLX controller.
 

Similar Topics

Hi Experts, Sorry as I am new in working with Allen Bradlly platform & Modbus Communication :bawling:. I have a redundant system ( Control Logix...
Replies
3
Views
5,128
How to architect and configure a redundant plc with with non redundant IO chassis (2nos) using 1756-EN2TR instead of control net. Whether i have...
Replies
1
Views
1,535
Hi, How to configure Control Logix DH+ to Ethernet Gateway ? I have 10 PLC's on a DH+ Network which say have node numbers from 1,2,3,4,...10...
Replies
2
Views
3,063
I have an injection molding machine that I'm trying to add a digital flow meter to the closed loop water cooling system. The flow meter is a...
Replies
6
Views
7,433
hi i have completed my program i want to download and run it with emulator can any one guide me how to check with emulator.
Replies
2
Views
3,859
Back
Top Bottom