I'm trying to comunicate two twidos using modbus tcp/ip, if is posible I'd like to have an example of ladder programming with the register used.

Thanks;

Ecoste
 
Last edited:
Hi there,

I have very little experience with Twido and maybe there is a propietary protocol for the PLCs to communicate over ethernet...

However, generally there can only be one master on a Modbus RTU/Modbus TCP network or rather 2 masters cannot communicate.
So If you are to use Modbus TCP, one of the PLCs needs to be configured as a Modbus TCP slave or If the PLCs needs to be masters, you could use a gateway (Modbus slave to Modbus slave).


My 2 cents
 
Hi Pudden,
Thanks for response, Modbus is the protocol that schneider use for comunication. It can be RTU, ASCII or TCP/IP. Like you are mensioning, you can configure a master and the rest as slaves. Until that point I´m OK. But when trying to edit my ladder (for twido), in the master, I´m not sure if I have to use the same format, as in RTU modbus, for messages instructions, or registers representations.

ecoste
 

Similar Topics

Hello, all! I'm on the cross-roads between applying for the: PE in Controls Systems - https://ncees.org/engineering/pe/control-systems/ and PE in...
Replies
7
Views
3,786
let's say I am developing my own PLC. I have schematics and I want to pass to PCB production. But I am new in electronics and I need to check my...
Replies
3
Views
1,866
Hi, Does anyone have any experience with hydraulic fluid static electricity affecting electronics?
Replies
2
Views
1,763
Hi All, i know technically not a PLC, but you guys have a wealth of knowledge that maybe someone will be able to help in this subject. i have an...
Replies
1
Views
1,420
Could any one explain me regarding the EDS file of a devicenet device. I am trying to understand. My question is Input 1 : it says it should be 8...
Replies
0
Views
1,559
Back
Top Bottom