I can't get the Simatic FB14/15 to work between two Siemens
S7-300 CPs, PLC1 and PLC2.
So far I have tried the following:
01) Configured profinet and changed the connection from PLC1
to PLC2 to yes.
02) On PLC2 configured:
a) A shared datablock 1001 with one entry.
b) A network wich maps to that one entry in 1001 and set it.
03) On PLC1 configured:
a) A shared datablock 1001 with one entry.
b) In OB1 I use the FB14/15 from the standard system library.
c) Enabled debugging bits on FB14/15.
The result when monitoring:
01) On PLC1 in DB1001 the entry 0.0 value is true.
02) On PLC2 in OB1 the network with the FB14 block is true and
the bit for activating the readout is true.
03) On PLC2 in DB1001 the entry 0.0 value remains false.
04) No connection error or read error occurs.
I am stuck on this simple step which at the end of the day turned
out to be not as simple as I thought.
Your help is much appreciated.
Regards
S7-300 CPs, PLC1 and PLC2.
So far I have tried the following:
01) Configured profinet and changed the connection from PLC1
to PLC2 to yes.
02) On PLC2 configured:
a) A shared datablock 1001 with one entry.
b) A network wich maps to that one entry in 1001 and set it.
03) On PLC1 configured:
a) A shared datablock 1001 with one entry.
b) In OB1 I use the FB14/15 from the standard system library.
c) Enabled debugging bits on FB14/15.
The result when monitoring:
01) On PLC1 in DB1001 the entry 0.0 value is true.
02) On PLC2 in OB1 the network with the FB14 block is true and
the bit for activating the readout is true.
03) On PLC2 in DB1001 the entry 0.0 value remains false.
04) No connection error or read error occurs.
I am stuck on this simple step which at the end of the day turned
out to be not as simple as I thought.
Your help is much appreciated.
Regards