I was wondering what is better a signal coming into the plc with 1 - 10 milli volts or one that sends 0 - 20 milli amps
what are the good and bad of both.
 
Generally most instrument engineers prefer a "4-to-20 miliampere" signal, because it has a defined non-zero minimum input of 4 miliamps. If the signal is lost due to a disconnected wire or other failure, then you can detect that with a simple miiiammeter test. For the other voltage methods, a "0" input might mean an actual 0 signal, or it could be a disconnected wire. A disconnected current signal will normally show an open circuit reading, which can also be confusing.
 
I try to go for 4-20mA when I can.
In addition to the reasons given by Lancie1, I have also have the following reasons:
*4-20mA seems to be the best for noise immunity
*It is very common, and most instrument manufacturers have instruments in this range
*Lines often get milivolt range noise in them, so using a milivolt range gets a low signal to noise ratio

In addition, devices are now more commonly fitted with Bus systems.
For analog devices, you may find it better to use Profibus, Devicenet or ASi 2. This also gets you better diagnostics.

Hope this helps,

Doug
 
Also with 4-20 you do not have to calculate the voltage drop for the length of wire your using.


Ken

"The older I get,
the better I was"
 

Similar Topics

Hello all, I know its not good practice to have duplicate destructive bits when writing plc code, but I'm wondering about writing to the same tag...
Replies
2
Views
129
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
57
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
542
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
Replies
1
Views
158
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
Replies
5
Views
139
Back
Top Bottom