Hi, I've hard-wired an 9,000BTU window A/C unit so that it can be operated via my PLC. So what I do is turn ON the compressor and fan using a couple of relays when I need to bring the temperature down.
I have a Vaisala HMT100 temperature/humidity sensor hooked up to an Allen Bradley MicroLogix 1400 PLC with a 0-20mA analog module.
It seems to me that a PID is mostly designed to control a process that is affected by a variable device (i.e. valve, heating element, fan, etc) where opening/intensity/level/speed/etc can be adjusted, so as to achieve an almost perfect SP.
So since the compressor is either turned OFF or ON at any given time, does it still make sense to us a PID? Should I just use logic to compare the SP to manually keep the compressor ON/OFF using ladder logic. So for example if the SP is 25 degC, should I just turn the compressor OFF when the temperature lowers to 25.2 and turn back ON when temperature reaches 25.8, for example.
I'm still learning about how to tune PIDs, so please bear with me if what I'm asking doesn't make sense and it's obvious to an experienced PLC programmer to always use PIDs, even in situations like this.
Some information: The SP=25 degC and it takes about 25 minutes to bring a temperature of 30 degC down to the setpoint (as shown in below image).
Any thoughts?
Thanks in advance!
I have a Vaisala HMT100 temperature/humidity sensor hooked up to an Allen Bradley MicroLogix 1400 PLC with a 0-20mA analog module.
It seems to me that a PID is mostly designed to control a process that is affected by a variable device (i.e. valve, heating element, fan, etc) where opening/intensity/level/speed/etc can be adjusted, so as to achieve an almost perfect SP.
So since the compressor is either turned OFF or ON at any given time, does it still make sense to us a PID? Should I just use logic to compare the SP to manually keep the compressor ON/OFF using ladder logic. So for example if the SP is 25 degC, should I just turn the compressor OFF when the temperature lowers to 25.2 and turn back ON when temperature reaches 25.8, for example.
I'm still learning about how to tune PIDs, so please bear with me if what I'm asking doesn't make sense and it's obvious to an experienced PLC programmer to always use PIDs, even in situations like this.
Some information: The SP=25 degC and it takes about 25 minutes to bring a temperature of 30 degC down to the setpoint (as shown in below image).
Any thoughts?