set maxEU in tag on Intouch Wonderware

b_e33

Member
Join Date
Mar 2013
Location
lolo
Posts
59
i want to set value of Tag into enother Tag but to is max EU value
so i read about it and i understand that i need to write:
Tag.maxEU=Tag;

but it is not work
how can i set the Tag.maxEU from enother tag value?
 
I just saw in their manual that the M of MaxEU is in capital, so maybe that's what is causing the error. So you should use "Tag.MaxEU".
 
I based my comment on the InTouch Reference Guide, relevant page attached.
 
This is with V9.5, don't know if it's any different with a newer version.
.
.

untitled.JPG
 
Check the tag configuration in tag name dictionary.
Is the tag "TestValue" configured "Read/Write" or "Read Only"? Should be "Read/Write".
 
Last edited:
Check the tag configuration in tag name dictionary.
Is the tag "TestValue" configured "Read/Write" or "Read Only"? Should be "Read/Write".

Fair point, you would get this error if you tried to assign a value to a read only tagname but in this case TestValue is a Memory Integer which is always Read/Write.

I was just illustrating that the MaxEU dotfield was read only.
 

Similar Topics

Hello, I still do not have equipment in to test. But the RTAC ladder does not have a timer reset coil. I wonder if a reset coil on Timer.IN is...
Replies
1
Views
109
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
Replies
0
Views
48
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
375
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
108
I was loading a program onto an XE1e2 PLC and it got stuck on these two windows and won't progress. It won't let me connect from the PC to reload...
Replies
0
Views
96
Back
Top Bottom