ok so i go called over to help the instrument mechanics trouble shoot a valve not working. I'm using a PLC 5 and the analog output cards are "1771 NOC A" analog out put cards. the operator has the PID control in manual putting in a manual set point to PD80:5.SO to the valve. It wouldnt change the value no matter what he typed in. so i got the instrument mechanics to remove the wires to the field and sure as all hell the PLC wasnt changing values, it was stuck at 15mA even if i changed the value in I/O config. i could even see the operator changing the value and it was sending out the appropriate mA but still was stuck to 15 mA on the card. So i decided to change to a different output card which had spare address's. So i took the value from PD80:5.SO and inserted a new rung and did a move instruction and used the source as PD80:5.SO then the destination to the new adress N44:34. I had to scale the out put from 0-100 because thats what he uses in the HMI. Everything seems to be working as far as the move i can see it put the data in the new channel but there is nothing coming out of the card! i have hooked up the signal generator and put it into read and nothing. and i know my points are correct on the card. I can see under I/O config under that card and channel its saying its sending out 12 mA at 50. Do you have to enable the analog channel that was not used before after i scaled it? is there some kind of configurating im missing. As of now i have the singal generator hooked up and manually sending signals to the valve with that until i can get this going! PLEASE HELP,
 
I figured it out, I didnt accept the new edits and had the configuration enable box still checked in the I/O config. once I unchecked the box and enabled edits it began to write to the card. I'm Happy again
 

Similar Topics

please help me . I have to make this ladder diagram and I can’t figure it out :(
Replies
12
Views
308
Hello, I am trying to get a Yokogawa Hart pressure Transmitter and a Rosemount Temp Transmitter to read on a 1769-IF4 module on an L33ERM...
Replies
10
Views
378
Please help me, I have solve many week but still not solve it. I found trouble of factory talk studio when I set tag by browse address of OPC...
Replies
0
Views
118
Hello Everyone, i Have im my Industry a Endress & Hauser Promag400 this has a screen that constantly have that error, it says to wait, somebody...
Replies
2
Views
479
Back
Top Bottom