S7314IFM communication with CP342-5 and CB15(VFD)

Join Date
Feb 2013
Location
karachi
Posts
17
I want to configure s7314ifm plc with cp module cp342-5. And after that I have to communicate cp342-5 with a vfd through profibus dp cb15. I don't know what hardware configuration should I use and how to communicate and operate it. I will use vfd as a slave but I am confused that either my plc 314ifm or cp342-5 which one will be used as master.
 
Hi,

The 342-5 will be the master, not the cpu.
As far as I can remember, the 314IFM does not have Profibus port, only mpi.
So you connect the 342-5 card to the Profibus network in netpro.
You have to do the same with your slave device. Then you go to properties on the cp card, and set it up as master...

A
 
I want to configure s7314ifm plc with cp module cp342-5. And after that I have to communicate cp342-5 with a vfd through profibus dp cb15. I don't know what hardware configuration should I use and how to communicate and operate it. I will use vfd as a slave but I am confused that either my plc 314ifm or cp342-5 which one will be used as master.

Click on the yellow "Downloads" tab above, then on "Siemens" and search for this doucment made by JesperMP:
[FONT=Arial, Verdana, Helvetica, sans-serif]"Some tips regarding Siemens Profibus DP via CP342-5.pdf "

Kalle


[/FONT]
 
I know that 314IFM only have mpi thats why I am using CP342-5. I am configuring the same as you described but my slave(CB15 for vfd) is not recognized and I don't know the way that how should I configure it with CP342-5.
 
Hello Sadiq;
The CP 342-5 is autonomous on the Profibus network (it works without prompting from the CPU), but to exchange the data between the CPU and the CP you must use the specific functions DP_Send and DP_Recv in your program, as shown in the following Siemens FAQ:
What should you watch out for when configuring a CP342-5 as DP master and why is it necessary to call the FC1 "DP_SEND" and FC2 "DP_RECV" functions in the user program of the CPU in order to transfer data? </B />

Hope this helps,
Daniel Chartier
 
thanks jrw. Now I have also set p918 but my cp342-5(master) is not recognizing my dp slave (cb15). Can you please tell me the steps that how should I communicate both of them my dp master and slave.
 

Similar Topics

Hi i have a s7 314ifm with some of the built in analogue inputs faulty.i want to put a analogue module on the end and change over the addrress in...
Replies
7
Views
2,099
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
Replies
0
Views
23
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
81
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
108
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
Replies
4
Views
145
Back
Top Bottom