I have an existing installation of panelview Plus 600 connected to SLC5/03 that has been working for the past couple of years. Recently the Panelview stopped communicating with the PLC. It gives errors across the top which are too small to read, but I suspect they say something about DF-1.
The Panelview only has a RS232 port, and the 5/03 has RS232 and DH485 (ethernet connector). So they comm between RS232 ports. I was able to get online with the PLC via DH485; I compared online vs. original program that I was given and they matched. I re-download the original program but that didn't help. I tried getting online with the PVP600 but I don't have RSLinx Enterprise so it showed up as a question mark. Another tech has RSLinx Enterprise and he was able to download the FTView program out of it, so I suspect the PVP600 RS232 port works fine.
I wasn't able to get online with the PLC via RS232, at first I suspected because it was configured to talk to the PVP600 on that port. When I looked at the channel config in the original program, both ports were selected DH485. That didn't seem right; seemed like the RS-232 port should be set to DF-1. So I matched what the other tech gave me for comms parameters that he used to get online with the PVP600, as follows:
(parameters for PVP600):
Device: PLC-CH0
Baud Rate: 19200
Parity: None
Stop Bits: 1
Station #: 00
Error Checking: CRC
Protocol: Full Duplex
I setup the PLC RS232 port as follows:
Driver: DF-1 Full Duplex
Baud: 19200
Parity: none
Control Line: no handshaking
Error Detection: CRC
Source ID: 0 (tried 0,1,2,3,4,5,9)
Embedded responses: enabled
timeout: 50
Retries, both: 3
Still would not communicate. I am wondering if I'm making a mistake by assuming that the protocol/parameters which worked between PVP600 and laptop for RSLinx & FTView are the same which should work between PVP600 and SLC5/03. Does the panelview use a different protocol to talk to computers than it does PLCs? Does it sound like I might have a bum port on the SLC5/03? I tried different cables between PLC and PVP600, straight-throughs and crossovers, no luck.
EDIT: to save you some time, I should inform you that I no longer have a working version of Factory Talk View Studio Machine Edition. As I said, I did not have RSLinx Enterprise; when I downloaded and installed Enterprise, it was an incompatible version and will not run, and will not allow FTView to run either. I am blind as to what is in the panelview program now.
The Panelview only has a RS232 port, and the 5/03 has RS232 and DH485 (ethernet connector). So they comm between RS232 ports. I was able to get online with the PLC via DH485; I compared online vs. original program that I was given and they matched. I re-download the original program but that didn't help. I tried getting online with the PVP600 but I don't have RSLinx Enterprise so it showed up as a question mark. Another tech has RSLinx Enterprise and he was able to download the FTView program out of it, so I suspect the PVP600 RS232 port works fine.
I wasn't able to get online with the PLC via RS232, at first I suspected because it was configured to talk to the PVP600 on that port. When I looked at the channel config in the original program, both ports were selected DH485. That didn't seem right; seemed like the RS-232 port should be set to DF-1. So I matched what the other tech gave me for comms parameters that he used to get online with the PVP600, as follows:
(parameters for PVP600):
Device: PLC-CH0
Baud Rate: 19200
Parity: None
Stop Bits: 1
Station #: 00
Error Checking: CRC
Protocol: Full Duplex
I setup the PLC RS232 port as follows:
Driver: DF-1 Full Duplex
Baud: 19200
Parity: none
Control Line: no handshaking
Error Detection: CRC
Source ID: 0 (tried 0,1,2,3,4,5,9)
Embedded responses: enabled
timeout: 50
Retries, both: 3
Still would not communicate. I am wondering if I'm making a mistake by assuming that the protocol/parameters which worked between PVP600 and laptop for RSLinx & FTView are the same which should work between PVP600 and SLC5/03. Does the panelview use a different protocol to talk to computers than it does PLCs? Does it sound like I might have a bum port on the SLC5/03? I tried different cables between PLC and PVP600, straight-throughs and crossovers, no luck.
EDIT: to save you some time, I should inform you that I no longer have a working version of Factory Talk View Studio Machine Edition. As I said, I did not have RSLinx Enterprise; when I downloaded and installed Enterprise, it was an incompatible version and will not run, and will not allow FTView to run either. I am blind as to what is in the panelview program now.
Last edited: