modbus rtu to TCP

teh

Supporting Member
Join Date
Nov 2002
Posts
140
hi folk,

I try to link up the kaeser compressor with Modbus RTU and using RED Lion convert it into Modbus TCP and after that link it to intouch wonderware.


do u know the kaeser Modbus communicator unit is using 4 wire or 2 wire?


I have attached the kaeser Modbus rtu pin assignment here..:mad:

IMG_2355.jpg
 
i would like to link in RS485... with red lion... below is connection of red lion

IMG_2356[1].jpg
 
Last edited:
No, it is not both, it is 2 wire 485.

When Rx+ and Tx + are combined on a single terminal, then it is "2 wire".

It appears that there are connections to +5v and/or ground for what I would call "biasing", but which they call "termination".

A Termination resistor is across the (+) and (-) data lines (at the ends of a multidrop network) and are used to dissipate the energy from a "reflection".

Most 485 devices have pre-installed bias resistors, this the first circuit I've seen with connection points

Why do you want to use RS-485, and not RS-232?
 
by this way.. is it the termination resistor MUST be connected in this RS485 loop?

danw, I use rs485 due to the distance...
 
my connection now

redlion-----------kaeser Compressor

1, 7 -----------------5---------------( TxB )

2,8------------------9----------------( TxA )

6--------------------1----------------Gnd


no termination Resistor 120ohm at terminal 1 , 2 ( Kaesor compressor )

I hv no put the resistor cause the Bandrate is set to 19200 only

would the circuit are ok?

I have try many days on this but no respond
 
Your termination seems to be ok.
Though terminal 1 and 7 seems to be connected internally. The same with 2 and 8.

Have you set parity, stop bits and baud rate in both the master (Red Lion) and the compressor, and have you given the slave (the compressor) a slave ID?
 
Datasheet

Does anyone have a datasheet for this Kaeser MOdbus module, I can't seem to find the info listing registers and pin out anywhere.

Thanks
 

Similar Topics

If a device has Modbus RTU over serial and Modbus RTO over TCP and Modbus TCP then there is a difference between Modbus RTU over TCP vs Modbus TCP...
Replies
7
Views
557
Looking to purchase some Modbus RTU to Modbus TCP gateways and was curious if anyone had any recent experience with specific brands they could...
Replies
5
Views
1,555
I have some instruments that are Modbus RTU and I want to communicate to them (read information) over Modbus TCP. What converters have you used...
Replies
8
Views
2,114
I successfully got a Micro 820 (Slave) and Red Lion HMI (Master) to work together using Modbus TCP. But now I need to add an Automation Direct...
Replies
3
Views
2,675
Hi all, how to connected modubus rtu master and 4 slaves and 2 tcp clients. kindly support me any one konws the solution.
Replies
12
Views
3,133
Back