Hi I have a fan that rotates at 2800rpm. I need to make sure that the fan is operating. I need to monitor the fan. It has an output that gives a signal 2*rotation so its 5600 pulses which is 933pulses per second. so I guess scan time will be a problem so I cant use normal inputs. The machine has a siemens s7-226. I have read the tutorial of this site so that is my level of expertise with plc programming. I have read the manual on the siemens 27-2xx and it tells me that there is a high speed counter HSC. with something like 30KHz so I guess this is what i need right?
Also do I just need to count 5600 every minute to know that my fan is working, reset the counter and then count again? it seems very easy.....too easy :) so what am I missing (please dont hurt me :p
 
Hej drenno.

Ahem.. 5600 pulses per minute is 93.3 pulses per second, not 933 pulses per second.
The problem may not be the pulse-to-pulse time, but the the pulse width. Depending on the sensor it can be very short.

Anyway, a dedicated counter input HSC seems to be the proper solution, also for the pulse-width.
You dont have to wait a full minute to read the count value. Every second would be possible depending on the requirement of your application.
 
Direct measurement of the air flow / DP is probably safest.. I had to check a sewage pond aerator the other day which wasn't making as much splash as the others, motor speed was fine, a blade had fallen off...If the fan is belt driven or variable pitch etc, can be a bit to go wrong down stream of the motor..

If you don't want to get into the S7, a standalone tacho style box should do the trick to give you a clean set of contacts..
 

Similar Topics

Hello everyone! I need to connect to a DL205-1 CPU and, as far as I know, I need to use DirectSOFT 6 software for the connection. Is anyone...
Replies
1
Views
66
Our punch press has a SLC500 with HELM weight module (HM-604-WM) for tonnage monitoring. The operator enters the weight range on the HMI, which is...
Replies
9
Views
203
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
Replies
0
Views
120
Good day, we have 15 analog inputs, we need to log the data in excel and monitor these values through web browser. We're planning to go with Delta...
Replies
1
Views
123
I have several plc’s that I’d like to monitor Into our SCADA when the comms break or plc faults. These are (SLC-505 & Compact Logic PLC’s) I...
Replies
6
Views
746
Back
Top Bottom