2011 NEC
210.5 Identification for Branch Circuits.
(C)Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit, where accessible, shall be identified by system. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
This means if you have 208/120 volt and 480/277 volt systems in a building you have to mark them differently.
Also from the NEC.
215.12 Identification for Feeders.
(C) Ungrounded Conductors.
(2) Feeders Supplied From Direct Current Systems. Where a feeder is supplied from a dc system operating at more than 60 volts, each ungrounded conductor of 4 AWG or larger shall be identified by polarity at all termination, connection, and splice points by marking tape, tagging, or other approved means; each ungrounded conductor of 6 AWG or smaller shall be identified by polarity at all termination, connection, and splice points in compliance with 215.12210.5(C)(2)(a) and (b). The identification methods utilized for conductors originating within each feeder panelboard or
similar feeder distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each feeder panelboard or similar feeder distribution equipment