I have an OEM panel that has 1 estop on the main panel door and 1 remote estop. Most controls are 24 volt but there is one 120 volt output card.
They have 120 volts ac going through both estop buttons which are the key locking type that have to be reset with a key.
The estops drop out the coils on 2 AB safety relays /contactors and they break 120 volts feeding the ac output card and 24 volts feeding the dc output card.
They have no reset button as soon as you pull the estop out the safety relay / contactor has power again but when i't actuated it does give an input to the plc that estop was hit and outputs turn off in the plc and it drops out the start logic in the plc so the machine has to be restarted.
Looks like they are using the locking estop as their method of reset but things could restart when it's pulled back out if for some reason the plc did not get the input to drop out the start / hold logic in the plc.
Is this really safe? Just want opinions on the design. I think we may need to change it?
They have 120 volts ac going through both estop buttons which are the key locking type that have to be reset with a key.
The estops drop out the coils on 2 AB safety relays /contactors and they break 120 volts feeding the ac output card and 24 volts feeding the dc output card.
They have no reset button as soon as you pull the estop out the safety relay / contactor has power again but when i't actuated it does give an input to the plc that estop was hit and outputs turn off in the plc and it drops out the start logic in the plc so the machine has to be restarted.
Looks like they are using the locking estop as their method of reset but things could restart when it's pulled back out if for some reason the plc did not get the input to drop out the start / hold logic in the plc.
Is this really safe? Just want opinions on the design. I think we may need to change it?