PeterW
Member
I'm working on a project where a Control Logix PLC will be upgraded to become a redundant PLC.
The CPU Rack will be duplicated and has two ControlNet cards (one to supervisory and one to IO) as well as an Ethernet card.
The existing CPU rack also contained two DHRIO cards, these are being moved to a non redundant IO rack on the ControlNet IO network.
The problem I'm looking at is the fact that these DHRIO cards have SLC's connected as part of the DH+ networks.
The ControlLogix reads data using a message instruction, this is no problem to adjust the map route.
The problem is the SLC's read data from the ControlLogix (site standard PLC's only read). The SLC message instruction only points to the DH+ card. Reading up on the DH+ card, I see you can use RXLinx to configure the card to tell the DH+ card where the CPU is, but this only appears to be able to point to the CPU slot number, not the full path that I will now need.
This makes me think that the DH+ card, must be in the same rack as the CPU to enable the SLC to access the CPU tags with a message instruction.
I can't really try this out to see if this is the case until I get to0 site during the change-over, which obviously will be too late for me to do anything about it if I cannot enter a path.
Anyone ever done this and can you put a path?
The CPU Rack will be duplicated and has two ControlNet cards (one to supervisory and one to IO) as well as an Ethernet card.
The existing CPU rack also contained two DHRIO cards, these are being moved to a non redundant IO rack on the ControlNet IO network.
The problem I'm looking at is the fact that these DHRIO cards have SLC's connected as part of the DH+ networks.
The ControlLogix reads data using a message instruction, this is no problem to adjust the map route.
The problem is the SLC's read data from the ControlLogix (site standard PLC's only read). The SLC message instruction only points to the DH+ card. Reading up on the DH+ card, I see you can use RXLinx to configure the card to tell the DH+ card where the CPU is, but this only appears to be able to point to the CPU slot number, not the full path that I will now need.
This makes me think that the DH+ card, must be in the same rack as the CPU to enable the SLC to access the CPU tags with a message instruction.
I can't really try this out to see if this is the case until I get to0 site during the change-over, which obviously will be too late for me to do anything about it if I cannot enter a path.
Anyone ever done this and can you put a path?