Welcome to the Forum !
The ControlLogix does not have built-in Status file tags like the PLC-5 and SLC-500 do.
Instead, it has system status and diagnostic objects that are accessible using the Get System Variable (GSV) and Set System Variable (SSV) instructions. These are well documented in the User Manual and in the Online Help, especially in the "GSV/SSV Objects" section.
There is not always an exact match between PLC-5 status objects and ControlLogix status objects because the two controllers have different operating systems. But we can get close.
In the PLC-5, S:8 is the "Last Scan Time" value, in milliseconds.
In the ControlLogix, the GSV instruction can be used to read the last scan time of a given Task. The GSV instruction will be targeted to the Task Object, and the name of the Task you want to read. The attribute will be the Last Scantime.
The scantimes in the ControlLogix are measured in Microseconds (.000001 second) instead of Milliseconds (.001 second), so you will have to adjust your logic to match.