I've got a SLC with a RIO scanner 1747-SN and a flex IO DIN rail 1794-ASB with an analog output module 1794-OF4I
Now I've found example code etc and read all the manuals fairly heavily however when doing the block transfer I keep getting error code -9 for the BTW and BTR indicating a block transfer timeout.
The 1794-ASB is flashing green which means it has the correct baud rate and is communicating, to confirm I change the dip switches to the wrong baud rate and the LED goes off.
If I had RS-485 comms to the remote IO scanner why am I getting a block transfer timeout? I've set the dip switches on the ASB to be logical rack 0, with the OF4I being the first module. This means it is logical rack 0, group 0, slot 0 (using full rack addressing).
I'm correctly setting the BTR word to be 000 for rack 0, group 0, slot 0. I've also tried setting the BTR word to be 100 and changing the dip switch to make it rack 1.
What else can I check? I'm pulling my hair out as I don't know what else can be wrong. Surely if I have the control word
The code I am using is example code recommended by rockwell support here, I've attached it as a zip also.
Any help would be muchly appreciated!
http://rockwellautomation-ap.custhelp.com/app/answers/detail/a_id/16036
Now I've found example code etc and read all the manuals fairly heavily however when doing the block transfer I keep getting error code -9 for the BTW and BTR indicating a block transfer timeout.
The 1794-ASB is flashing green which means it has the correct baud rate and is communicating, to confirm I change the dip switches to the wrong baud rate and the LED goes off.
If I had RS-485 comms to the remote IO scanner why am I getting a block transfer timeout? I've set the dip switches on the ASB to be logical rack 0, with the OF4I being the first module. This means it is logical rack 0, group 0, slot 0 (using full rack addressing).
I'm correctly setting the BTR word to be 000 for rack 0, group 0, slot 0. I've also tried setting the BTR word to be 100 and changing the dip switch to make it rack 1.
What else can I check? I'm pulling my hair out as I don't know what else can be wrong. Surely if I have the control word
The code I am using is example code recommended by rockwell support here, I've attached it as a zip also.
Any help would be muchly appreciated!
http://rockwellautomation-ap.custhelp.com/app/answers/detail/a_id/16036