Siemens ITC2200 displays

DLMUK

Member
Join Date
Jun 2013
Location
Southampton
Posts
311
Hi,

Has anyone ever used one of the Siemens Industrial Thin Clients before?

What I would like to do with it is:

S7-1200 PLC and 9" HMI at a local station
ITC2200 at a remote viewing point (about 150m away)

Am I correct in thinking that the ITC2200 can be configured to mirror the HMI screen?

Also, is 150m a suitable distance? I can install a switch if needs be.

Cheers,
 
It sounds like that setup should work. You will probably need the network switch you mentioned, because Ethernet cables are designed for a max length of about 100m.

You may also need a license for the HMI, to be able to view it remotely. If it is a Siemens HMI, then you will need the Sm@rtService license, or something like that. I haven't needed it in a while. If I recall, the HMI and Thin Client will always be on the same screen, and the HMI can only be operated at one location at a time, either the local HMI or the remote thin client. Being active on one locks the other out.
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
8
Views
134
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
141
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
300
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
112
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
198
Back
Top Bottom