Hi,

I have the following situation:

I am using a PV plus (latest firmware installed) programmed using FactoryTalk View Studio 8.

communication: Ethernet

The screen alarm is working fine (alarms are being displayed) however when I press acknowledge all or acknowledde alarm the PV screen goes blank and I have to power cycle. The other buttons such as up, down and silence are working fine

any suggestions ?

Thanks
 
The Acknowledge must be closing the Display that holds the Alarms, without having another display to go to. That gray background is what you see when FTView closes all the displays.

This is either some sort of race condition, or a mis-configuration of the Alarm display.

I always make my Alarm Display an "On-Top", not a "Replace". That way there will always be a display under it in case the Acknowledgement logic gets crosswise.

Also, there's a setting in the PanelView Plus configuration screen, as a Terminal Setting for Alarm functions. Select "No" for "Close Alarm Display When Newest Alarm Acknowledged".
 
The Acknowledge must be closing the Display that holds the Alarms, without having another display to go to. That gray background is what you see when FTView closes all the displays.

This is either some sort of race condition, or a mis-configuration of the Alarm display.

I always make my Alarm Display an "On-Top", not a "Replace". That way there will always be a display under it in case the Acknowledgement logic gets crosswise.

Also, there's a setting in the PanelView Plus configuration screen, as a Terminal Setting for Alarm functions. Select "No" for "Close Alarm Display When Newest Alarm Acknowledged".

Thanks a lot for your input. Helped me today. Cheers.
 

Similar Topics

Hey Guys, After a firmware upgrade and the addition of Viewpoint firmware on a panelview Plus 6, it will randomly promp the operator for a...
Replies
3
Views
1,670
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
88
I have 2 PV Plus 7 screens used in the same system that both have touch screens that can be challenging to activate after they haven't been...
Replies
0
Views
596
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
Replies
1
Views
753
Any good idea how to dim the display on a panelview plus performance serie b, at idel. Screen saver is not supported yet I have don it in global...
Replies
9
Views
2,270
Back
Top Bottom