I have a client with a requirement to keep a motor running in the event of a VFD failure. They do not have redundant motors, but will have redundant VFDs serving the same motor. This is the first time I've seen this and I am left wondering if there needs to be true isolation relays on the field (motor) sides of the VFDs isolating them from one another. Or, is it a non issue to have 1 VFD driving the motor while the other is commanded off with their motor terminals tied together electrically.
Some VFDs are designed to accomplish this, it is referred to as "N-1 redundancy". In effect, the VFD power section is split in two and run in parallel, each power section sharing equally and feeding the same motor. If one power section goes down, there are two choices of functionality:
- If the total drive power is matched to the motor size, the remaining power section is only capable of 1/2 of the motor power, so the drive automatically reduces the frequency to limit the motor current to what the drive can handle. This is often used in semi-critical pumping situations where SOME flow is better than NO flow.
- If the drive is designed as 2X the motor size, then either power section can power the motor fully, providing 100% redundancy without compromise. So normally both power sections are on and sharing the load, but if one goes down, the controller just disables the other and all of the power shifts over to the remaining drive seamlessly.
The key to this working is that there is ONLY ONE control board, so it is controlling BOTH power sections simultaneously and there is zero possibility of the outputs not matching. All it does when it detects a failure of one side is to stop giving it a firing signal.
In order to have two COMPLETELY separate VFDs running the same motor, the ONLY way to not have the drive transistors blow up is to have total isolation between them. If not, the psuedo-AC output from drive 1, if even SLIGHTLY different from that of drive 2, will cause the transistors in drive 2 to self commutate and vice versa, which will destroy them all. So you MUST have two isolation contactors, one on the output of each VFD, mechanically and electrically interlocked so that only one drive can be connected to the motor at the same time while not allowing the two outputs to "touch". The drawback to this is that because of the need for isolation between the drive outputs, there WILL be a time lag in switching from one to the other. That must be weighed against the reasons for requiring the redundancy.
Flying Start functionality would also be a requirement so that the backup drive can catch the spinning load, but most good quality drives have that now (under some name or another).
What size VFD / motor are we talking about here by the way?