Is it against code to mix voltages within one force guided relay? I have a force guided relay with a 24 VDC coil. This relay has five normally open contacts and one normally closed contacts. Two of the five normally open contacts are used: one to switch 208 VAC and one to switch 24 VDC. Is this allowed or just poor practice? My gut tells me the machine builder is just cheap and didn't bother separating the two circuits.

The coil for this force guided relay is switched using a safety PLC.
 
Im not sure with Canadian Rule, didn't find it in the code, but in general practice in building a control panel, is not to mix the power circuits with control circuits. First is safety, for your self and for the control circuits alike. There are some controllers in which input cannot be contaminated with EMF coming from the wires with high voltage
 
At least in the EU, yes you can mix voltages on adjacant relay contacts or aux contacts.
One should separate power and control circuits as best as one can, but you cannot achieve 100% separation.
 
Interesting.

If this would not be appropriate, how would you get feed back from a contactor?

If I have one contact from a pressure switch, controlling a 230 VAC valve, providing 24 VDC feed back to PLC and providing a pot free contact for another system, would I need to use 3 separate relays?

Would a 24 VDC be susceptible for EMF from 230 VAC (hardly high voltage?)

Just thinking out loud :)
 
Interesting.

If this would not be appropriate, how would you get feed back from a contactor?

If I have one contact from a pressure switch, controlling a 230 VAC valve, providing 24 VDC feed back to PLC and providing a pot free contact for another system, would I need to use 3 separate relays?

Would a 24 VDC be susceptible for EMF from 230 VAC (hardly high voltage?)

Just thinking out loud :)

I think normally we will assume the normally closed contact will switch 24 VDC for feedback to the safety PLC. Simiarly we will know the coil will be switched using 24 VDC. The problem I have is with the machine builder using the normally open contacts for different voltages. If I probe one set of contacts and measure 24 VDC then I wouldn't expect another set of normally open contacts to carry 208 VAC.
 
At least in the EU, yes you can mix voltages on adjacant relay contacts or aux contacts.
One should separate power and control circuits as best as one can, but you cannot achieve 100% separation.

This machine actually came from Germany so maybe it's OK. I am just wondering if there is anything in the US or Canadian electrical code to say this isn't allowed.
 
If I probe one set of contacts and measure 24 VDC then I wouldn't expect another set of normally open contacts to carry 208 VAC.


Why not? Isn't that why we use different colors of wire?
 

Similar Topics

We are in the process of designing equipment for Korea. The customer's supply voltage is 380V, 60 Hz. The motors on this equipment will be...
Replies
2
Views
2,190
We have a system using a Omron G5 Servo. The motor has failed and Omron has advised the delivery time 4 months for a new motor! I'm not overly...
Replies
3
Views
1,636
HI, In a mixing vessel tank, it was maintained with a product temperature of 70 degree. When vacuum applied to the tank, the product and jacket...
Replies
27
Views
5,294
Hi all, about to set up a flow loop in our garage that will be mixing oil and water for some water cut testing. In the past we've basically put a...
Replies
5
Views
1,487
Hello This is my first post on this forum, so bear with me. I'm working with a DeviceNet system where there needs to be a transition on the trunk...
Replies
5
Views
2,507
Back
Top Bottom