i would like to ask if adding a voltage regulator in plc can prevent current surges??
thank you
i would like to ask if adding a voltage regulator in plc can prevent current surges??
thank you
its like.. " everytime were having brown out.. the components of the machine will be damaged due to current surges".. so were planning to put a voltage regulator in the supply of the plc to prevent the IO card to damage..is it ok??..we dont have UPS in the machine..
It's fine. Use a high quality UPS that doesn't switch from line to battery... It must always be running off of the inverter.
veristors are normally used in main supply to prevent surges
the machine have 3 induction motors controlled by VFD nd PLC, and 5 solenoids...we use siemens s7 300 input module, output module, output relay module, and analog module to give signal to the VFD..the voltage regulator we used is from 440 to 24vdc.... we dont have UPS in our system just a voltage regulator.we have not use fused terminal block.. Last month one of our input module has been damage.. so we replace it with a new one.. after 2 weeks of operation, the output relay module has been damage so we replace a new..And finally this week, one of the induction motor don't reverse...so what im thinking now is that the analog module has been damage...I think its all about surge problem..I hope my manager will listen this time to my recommendation...haha
So many things are wrong with that answer.its like.. " everytime were having brown out.. the components of the machine will be damaged due to current surges"..
First, low voltage never damages electronics. All properly designed PLCs include voltage monitors. Voltage is perfectly fine even when so low that incandescent bulbs dim to 50% intensity. If voltage is lower, that monitor simply powers off a PLC - no damage. If that monitor does a power off, then it also delays a power on. Only assumed is an anomaly that also must not hamper any properly designed PLC. More likely, the anomaly is something completely different.rj061991,
#1 brownouts have two parts: the voltage sag and the voltage recovery.
Voltage suppressors work in reducing the damage caused by the recovery part of the brownout. I learned this first hand from an industrial plant 2 hours from work. Two times in a week the plc lost its program in a brownout.