PNP sensors vs dry contact sensor

Charbel

Member
Join Date
Jan 2012
Location
Beirut
Posts
307
Dear,

I was wondering which one is better to use a PNP sensor or a dry contact sensor,
I was checking the inductive sensor from Schneider electric XS4p12PA340, it is a 3 wires PNP sensor,

to connect it, it needs sinking inputs (NPN) and they are available from many PLC manufacturers,

my question is, is it better to convert it so it has dry contact (by adding to it a relay module), so that it can be easier for connection and troubleshooting.

I really appreciate any thoughts on this.

regards,

charbel
 
dear,

thank you for your feedback, one final thought, what about having a 2 wire inductive proximity switch instead of having to put a relay module in between, for ease of connection and troubleshooting?
 
Dear Osmanmom,

the question was if it is better to use a proximity swtich with PNP output or use a 2 wire proximity switch.
 
dear,

thank you for your feedback, one final thought, what about having a 2 wire inductive proximity switch instead of having to put a relay module in between, for ease of connection and troubleshooting?

A relay in-between what?
For a three wire sensor, the sense lead is usually directly connected to your PLC input, and the input module shares the same common as the sensor.

For a two wire sensor, you connect the output lead to the PLC input, and the input module shares the same common as the sensor power supply.
 
time matters

If it needs to work fast or cycles often don't use a relay, it is only one more point of failure.
If it is for switchs that are used for trouble points and you can't see the lights on the prox switch, a relay with pilot light can help in troubleshooting ( look for all lights on or off ).
 
Why not simply purchase an NPN version of that sensor? Driving a relay with your PNP sensor and switching your NPN PLC input is certainly possible, but why go to all the trouble when you can simply purchase the right sensor for the application?



-rpoet
 
Dear all,

thank you a lot for your replies, the intent was to see (technically or better over long run) which one is better to use a proximity switch with PNP output or use a 2 wire proximity switch, the application is for valve position (either opened or closed).

now it is clear to me that better to choose a proximity switch with PNP output.

Thanks!

Charbel
 

Similar Topics

For example, I need to choose PNP sensor for a Sink PLC input. Also do Sinking/Sourcing PLC inputs relay to the PLC reading? e.g. PNP sensor for...
Replies
27
Views
19,698
Hi, So, I eventually got a zelio to work with. 2 silly questions: Do I need a manual push button as an input to the smart relay to make it start...
Replies
2
Views
2,720
guys i am trying to learn sinking and sourcing concepts and need some clarification . the way i understand is pnp sensors switch + side of dc...
Replies
13
Views
5,583
D
Hello guys, I need more some clarification on wiring sensors. From what I have read this is what I understand: Typically an NPN sensor has the...
Replies
15
Views
16,056
Doing a little quick research/info gathering. The opinion is that NPN is more popular in the US and PNP is more widely used in Europe. Would you...
Replies
10
Views
15,710
Back
Top Bottom