AB 700 flex drive

cat60daddy

Member
Join Date
Oct 2015
Location
Detroit, Michigan
Posts
4
AB 700 flex troubleshooting: My VFD is intermittently faulting out my roll table Euro drive motor. I receive a Output phase loss fault (code 21). I switch over to my standby 700 flex, and 3 hours later the same fault. No information in the manual to help. Has anyone experience this please respond. :cool:
 
AB 700 power flex

Ok, that a start, but I have already replaced the Euro drive SEW motor with a new one. Are you suggesting to ring out the leads going back to the VFD, and or control relay contacts.:cool:
 
Shouldn't be any relay or contactor contacts in the motor leads, as a general rule.
Yes, but "roll table" and "Eurodrive" evokes a vision of something from Europe with EU safety circuits that, if SIL4, might have an output safety contactor(s) between the drive and motor. A burned contact on that contactor would do it.

What I see happen is that the design INTENT is that the safety contactor is only used in a safety procedure, when the drive is supposed to already be turned off under normal operating procedures. But lazy operators figure out that if they just open an access door or something, the safety circuit shuts the drive down and they dont have to take 3 steps to the right to hit the stop button for a normal shut down routine. The constant opening of that contactor on the output of the drive sets up a race to see who will fail first, the contacts or the drive transistors. But the operators couldn't care less...
 

Similar Topics

I've got 7 Powerflex 700 drives running a varying number of motors on each drive. I have one drive that is consistently running higher speed than...
Replies
3
Views
1,893
I have a current program where we are monitoring the Amps on a motor, Output Current parameter 3, however it's actually linked to parameter 4...
Replies
4
Views
2,762
Hello, I am having an issue with a Powerflex 700 drive faulting intermittently (but regularly) on port adapter 5 (code 75). The fault text says...
Replies
15
Views
24,838
We have a Busse De-Pallitizer Hoist 10hp Motor with an allen bradley powerflex 700 vector drive with encoder and brake. During the high speed up...
Replies
6
Views
4,876
I am using a PowerFlex 700 A/B drive with a 10 hp inverter motor. when I run at slow speeds it runs fine but when I turn up the load on the motor...
Replies
7
Views
4,104
Back
Top Bottom