Linking tag to drive parameter powerflex 70/700
remullis
Oct 2012
Georgia
179
I have a current program where we are monitoring the Amps on a motor, Output Current parameter 3, however it's actually linked to parameter 4 which is the torque current.
First question is which should I be monitoring for reliability maintenance and how to I edit this tag to look at the correct one?
RSlogix to Powerflex 70
Rich
Basically, change the PowerFlex drive parameter number in your tag, from "004" to "003". See the attached picture.
For maintenance, I think you would want to see the total current, which includes non-torque current. Current that is not producing torque could be due to voltage supply problems or low power factor. You might want to set up a tag to monitor Parameter 008, the motor power factor. A low power factor (less than 0.90) costs money in increased power bills in the long run.
Yes we use 4 datalinks A1,A2,B1,B2 and we configure all drives as follows:
310 = 1 (freq)
311 = 3 (Output Current)
312 = 4 (Torque Current)
313 = 243 (Fault Code)
I will check this out. Thanks Rich
310 = 1 (freq)
Rich, In the case where you already have both currents IN your PLC, then all you need to do is search for the "312" RSLogix tag in your PLC program, and replace it with "311" at the place where it is used to display motor amps. You may not want to replace all cases of where you find "312" because it is possible that the torque current is being used for other purposes.
I would like to cause an HMI tag to change value (digital) when a certain PLC tag changes value. Is there a way to do this? Specifically I would...
1,916
I am trying to use tag based alarms in Studio 5000. It seems really great at making alarms automatic. I have a few alarms that require...
1,062
Hello, Does anyone know of a way to hyperlink RS5K Tags into Microsoft Word or Outlook? It would be nice to be able to link a Tag in an Email or...
1,378
I maybe have a stupid question, but... This is what I did: I have an automatic screen and a manual screen, when there is an alarm active, then...
7,108
So I'm currently in the process of linking 2 1756-L72 processors to send alarms back and forth. One processor is rev 26.13 and the other is 32.11...
128