Prosoft 3100_3150_MCM-Modbus Address

Seyed Mohamed

Member
Join Date
Apr 2015
Location
Al khobar
Posts
39
Dear Gents,

I have a PLC5/30 receiving data from Bently (Vibration Monitoring Unit) using port-1 and sending data to DCS using port-2. I have the following modbus configuration in PLC side.

PORT1-Master RTU (1 stop bit, odd parity,19200 Baud Rate)
PORT2-Slave RTU (1 stop bit, even parity,19200 Baud Rate, slave id-1)
Read data block count:14
Write data block count:9
Read Block ID Start:9
Write Block ID Start:0

As we can find the modbus address 30201 to 30439 & 12401 to 12490 configured using port2 as slave with dcs.

Can any one please tel me what is the modbus address configured using port1.

Thanks.
 
I would contact the manufacturer of the Bently (Vibration Monitoring Unit) GE and get the modbus manual for the unit. This will show the modbus addresses you are looking for.

Hope this helps,
 

Similar Topics

I have PLC5/30 system having modbus communication with VMS and DCS. i Have the logic backup alone. Anybody please tell how to find the modbus...
Replies
0
Views
1,233
Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
0
Views
42
Hi, We have an application that has a device that goes through a reboot (appears un-graceful) What then happens is the MVI module appears to hang...
Replies
0
Views
90
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
127
Hello. I am trying to use a Prosoft AN-X4 to improve the communications for a new panelview plus 7. This is going from a SLC-500 through DH+ to a...
Replies
9
Views
307
Back
Top Bottom