userxyz Member U Join Date May 2002 Location any Posts 2,768 Nov 16, 2015 #1 I cannot make a connection that is integrated in the TP900... Could the reason because of using a 300 CPU in Tia Portal ???
I cannot make a connection that is integrated in the TP900... Could the reason because of using a 300 CPU in Tia Portal ???
JesperMP Lifetime Supporting Member + Moderator Join Date Feb 2003 Location ᚴᚬᛒᛅᚾᚼᚬᚠᚾ Posts 16,322 Nov 16, 2015 #2 in TIA, go to Devices & Networks, and check that both PLC and HMI are connected to the same network.
mk42 Lifetime Supporting Member M Join Date Jun 2013 Location MI Posts 3,280 Nov 16, 2015 #3 In the devices and Networks view, select Connections on the left side, then make sure that HMI connections is selected in the dropdown. Then drag from the HMI to the PLC.
In the devices and Networks view, select Connections on the left side, then make sure that HMI connections is selected in the dropdown. Then drag from the HMI to the PLC.
userxyz Member OP U Join Date May 2002 Location any Posts 2,768 Nov 16, 2015 #4 Hello Hello, It is the case: But still I cannot make an integrated connection. Kind regards, C
userxyz Member OP U Join Date May 2002 Location any Posts 2,768 Nov 16, 2015 #5 Ow Ow, After selecting HMI Connections I still had to draw the connection, understood. Thanks guys, Regards, C
Ow Ow, After selecting HMI Connections I still had to draw the connection, understood. Thanks guys, Regards, C