PanelView 600 + PLC5/40 RIO COMM

ddsiller

Member
Join Date
Nov 2015
Location
Arizona
Posts
19
Hi there,

I have a PannelView 600 connected to a PLC5/40 RIO. But they are not communicating.


I have set the PV600 Communication in PannelBuilder32:
Rack Number: 1
Rack Size: 1/4
Starting Group: 0,1
Pass--Trough Enabled: Yes
Last Chasis: Yes
Baud Rate: 57.6K

I have set my PLC5/40 in Rslogix 5:
Channel 2B - Scanner Mode
Rack Number: 1
Rack Size: 1/4
Group: 0
Baud Rate: 57.6K
 
Those settings look appropriate.

Rule #1 with DH+ or RIO devices is to switch the blue and clear wires if they aren't communicating.

How long is the cable ? Did you install 150 ohm terminating resistors ?

In general a PLC-5 will detect a PanelView Standard with the Autoconfigure feature on the RIO channel if it's connected correctly.
 
Those settings look appropriate.

Rule #1 with DH+ or RIO devices is to switch the blue and clear wires if they aren't communicating.

How long is the cable ? Did you install 150 ohm terminating resistors ?

In general a PLC-5 will detect a PanelView Standard with the Autoconfigure feature on the RIO channel if it's connected correctly.


Ken That solved my problem.
I switched Clear and Blue and worked perfectly. I was using the same cable with a PowerFlex 700 and the Same PLC5 without switching and it was working great.

Where can I find more information about Cable Configurations? Or could you explain me why or why not switching? That would make my life much better.
 

Similar Topics

I'm replacing a DL40 display with a PV+600. Quite brave of me as I've not used much AB stuff. The DL40 display uses DH+ channel B to communicate...
Replies
20
Views
7,471
I am a student working on a school project and I am really new to both the PLC programming and PanelView so excuse me if this is a dumb question...
Replies
3
Views
7,198
I am trying to go to a 504 CPU. and on my hmi I am getting a 9028 error. can someone explain what they mean by change reference?
Replies
12
Views
220
Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
Replies
10
Views
461
Hello, Friends Please someone help me find right cable to communicate Panelview 600 (2711-B6C9) to Micrologix 1200 (1762-L24AWAR). AND any advice.
Replies
3
Views
269
Back
Top Bottom