HI there,
I am a beginner with PLCs.
I have a PLC5/40 Allen Bradley with 1771 IAD & OAD (Output and Input Modules in the same Chasis) and a PowerFlex 700 AC drive. I am using RSlogix 5 with DH+ to USB connection. I have already setup the PLC with mi PC and is working fine. I made a simple program to send an input signal to open the output signal. The issue is that I wired the physical Outputs to the PowerFlex 700 and I can't start the drive trough my PLC. A fault occurs "Stop asserted" which clears when I toggle the stop input from my PLC activating the Stop signal of my drive . I can start the drive trough the HIM and stop it from my PLC but I cant start the Powerflex 700 from my PLC
I am a beginner with PLCs.
I have a PLC5/40 Allen Bradley with 1771 IAD & OAD (Output and Input Modules in the same Chasis) and a PowerFlex 700 AC drive. I am using RSlogix 5 with DH+ to USB connection. I have already setup the PLC with mi PC and is working fine. I made a simple program to send an input signal to open the output signal. The issue is that I wired the physical Outputs to the PowerFlex 700 and I can't start the drive trough my PLC. A fault occurs "Stop asserted" which clears when I toggle the stop input from my PLC activating the Stop signal of my drive . I can start the drive trough the HIM and stop it from my PLC but I cant start the Powerflex 700 from my PLC