Delta V with S7 300 CPU via Profifbus
teh
Supporting Member
Nov 2002
140
Dear Folk,
Can somebody give me the idea / advise on how to configure the CPU 315-2DP ( Slave ) to talk to Emerson Delta V via Profibus DP.
How to configure it?
i have try configure it at hardware configuration, but fail.
Can it just direct talk with s7 300 CPU?
or
I need additional CP 342?
Regards
nonuke
He needs no GSD from Siemens side since S7 is slave. GSD file shuld be loaded into Delta V since thats Profibus master!
I saw similar topic in this forum. Find it, JesperMP gives link to Siemens Support page that may be very helpfull.
Thanks. I have been successful in establishing communication between Delta V and S7 314 PLC. Now I am trying on S7 313C with CP 342 DP slave.
Ramesh
Hi Folks,
I have success link between both ( Delta V , master Siemens , Slave Via Profibus ).
Following is some documentation going share with u guy..
General requirements
the following needs to set up in the PLC:
  • Baudrate ( max. 1.5Mbps)
  • DP-Slave Address ( 2..126)
  • Slot Addresses (1..32)
  • The slot configuration for the application
Configuration Parameters
Slot Configuration
In DeltaV first 3 slots are to be created for 1st, 2nd and 3rd general ID and are reserved. These 3 slots with no I/O signals are required to be configured in DeltaV for housekeeping purposes. These slots are not configured in the PLC. DeltaV user data slots start at slot 4. PLC user data definition starts from slot 1. The slots assignments for the user data in DeltaV and the PLC must match.
Tables 3.1 and 3.2 describe the various slot types that can be configured. The slot definition comprises of 3 parts: part 1 defines the direction of data transfer, I stands for Input and Q stands for Output, part 2 defines the slot length and part 3 defines the data format. E.g. Slot definition Master_I Slave_Q 4 B tot lgth means this is Input to Master and Output(Q) from Slave and has 4 Bytes of total length.
DeltaV Output Slot configuration
Slot configuration limiting values
In DeltaV maximum of 32 slots per PLC for user data exchange can be configured starting from Slot 4 to Slot 35. These Slots can be freely mixed. However the same sequence and slot type should be available on the PLC for communication to be established and these are numbered from 1 to 32. Following table lists the maximum data exchange for a PLC over Profibus.
Description
Limit
Maximum number of Slots per CPU
32
Maximum length of data per Slot
32 Bytes
Maximum number of Input bytes per CPU
244 Bytes
Maximum number of Output bytes per CPU
244 Bytes
Data Types Supported
As described in the earlier tables DeltaV can exchange range of different data formats with the PLC. All the data types in DeltaV are supported by S7-PLC. The various data types can be freely mixed in a given slot. Analogue values in Floating point format and digital signal combined as bit coded byte or word can be mixed in one slot.
Data word bit order
If digital signals are stored in the data words in Data Blocks in PLC and exchanged over the Profibus care should be taken as construction of data word is different. Please note the byte offset while accessing this digital information. The PLC accesses the bytes in Data word DW0 as DB0 and DB1 where as those are Byte offset 1 and 0 respectively. Following diagram shows the sequence of bits in a data word.
DW0
DB0
DB1
Note: When such bit combinations are used confirm this with the PLC programmer about the byte offset.
PLC Memory allocation
The CPU of the PLC operating as a DP-Slave provides an intermediate memory for the data exchange. Up to 32 Address areas (slots) can be configured using Siemens Programming tool. That is, DeltaV writes its data to these intermediate memory address areas (slots) and CPU reads this data in its user program and vice-versa.
Following table shows the principle of address areas (slots) This is done using Siemens Programming tool.
Type
Master Address
Type
Slave Address
Length
Unit
Consistency
I
222
Q
310
Byte
Unit
Q
I
Word
Total length
32
Address Areas in the DeltaV
Address Areas in the DP Slave CPU
These address area parameters must be identical to DeltaV Slot definition
In the PLC configuration 32 slots can defined for user data exchange and they need to match DeltaV configuration. The Type I stands for Input and Q stands for Output. Output from DeltaV is Input to PLC and vice-versa. While assigning Master Addresses continuous addressing is to be defined for Inputs and Outputs. These addresses are not significant for DeltaV as there are no Address areas in the DeltaV.
Note : When the CPU of the PLC goes to STOP mode, data in the CPU intermediate memory are overwritten with “0” that is, DeltaV reads its inputs as “0”. However when the Profibus communication stops the CPU intermediate memory is maintained and the CPU uses the stale data. Therefore it is advised to have a life signal in the communication which takes care of this issue.
Configuration Rules
The following rules apply:
  1. It is mandatory to ensure the PLC and DeltaV slot configurations are identical (see section 3.1)
  2. Integer and floating point signals held in PLC data blocks must start on an even number byte offset. Values held in byte oriented memory can start on any byte.
  3. It is not necessary to configure all signals in DeltaV.
Configuring DeltaV
The following steps are required to configure an instance of a PLC in the DeltaV I/O database:
  1. Select the GSD file corresponding to the S7 hardware model from the Siemens internet site (see section 2.3)
  2. Add the S7 device to the DeltaV Profibus library
  3. Create an instance of a device on a Profibus I/O port
  4. Add slots to the device to match the PLC slot configuration
  5. Add the required signals to the slots.
An example of a DeltaV configuration is given in section 4.
Error reporting and recovery
In case of communication failure the status of the DST is set to BADNOCOM and it can be used in the Control Module for interlocking.
Recovery of communication with the PLC is automatic.
Dear Teh,
You documentation was very useful and I have been able to establish communication between 6 PLCs and the Delta V DCS. The only mistake I was doing was I was using the first slot of the DCS whereas it should have been the fourth slot. Rightly said by you, the first three slots are fixed and do not have any information.
Now, only one PLC is left. I will contact you further, if required.
Thanks again.
Ramesh
Hi Folks,
Slot Configuration
Description
Limit
32
32 Bytes
244 Bytes
244 Bytes
Data word bit order
DW0
DB0
DB1
Type
Master Address
Type
Slave Address
Length
Unit
Consistency
I
222
Q
310
Byte
Unit
Q
I
Word
Total length
32
Configuration Rules
Configuring DeltaV
Hi Teh, I was looking at your old reply in relation to DeltaV communication to a Siemens profibus slave and you refer to sections in a document but I can't find section 4 in S7-300.doc file (example of the DeltaV configuration as the Master). Can you please send it on.
Hi I need to setup a Delta MS300 VSD. I have not done something like this in years so any help would be appreciated. I am going through the...
1,294
hello dear we have a problem with communicate with delta dop hmi and siemens s7-300 cpu . we use ISO ON TCP connection and AG-SEND and AG-RECV...
3,510
One of the machines i reprogrammed a while ago started giving me communication error 14 on hmi. Sadly i could find about the error is the station...
4,568
Hello I am trying to communicate with Delta HMI DOP-b series with siemens s7-300 PLC. Can anyone guide me about this with connection (pin) details
6,494
I am using a Hyd. press with s7-300 PLC. When i tried DELTA HMI to interface with PLC as per the Delta Manual instruction. But the communication...
5,659