I'm trying to set up a 1746-HSCE2 high speed counter module in a SLC500 with a SLC 5/03 processor. The manual - http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um002_-en-p.pdf - gives an application example on page 6-7 using indirect addressing. However, when I try to verify the project, I get an error saying "Indirect addressing is not supported on the current processor type for the N file type".
The manual states that indirect addressing will only work with SLC 5/03 and higher processors. I have an SLC 5/03. The example in the manual also uses the N file type, so I don't know what the problem is.
The offending instruction is
COP
Source #N12:[N13:0]
Dest #O:5.0
Length 8
If anyone could offer any insight, it would be very much appreciated.
The manual states that indirect addressing will only work with SLC 5/03 and higher processors. I have an SLC 5/03. The example in the manual also uses the N file type, so I don't know what the problem is.
The offending instruction is
COP
Source #N12:[N13:0]
Dest #O:5.0
Length 8
If anyone could offer any insight, it would be very much appreciated.