Is it possible to hold the Electrical "Contactor" using a Single pulse of Sensor...???
I want to hold the "Contactor" using a single Pulse of the sensor.. Please help.
Kapil,
Yes, it is possible to cause a contactor to be held ON due to a single pulse from a sensor. However, you will need some other equipment (other than the sensor pulse and the contactor).
Please list the equipment that you are using. Because you came to a PLC site, I assume that you are using some PLC brand, model, and catalog number. If you list the brand of the PLC, the contactor, and the sensor, and state how long that your sensor input is ON, then we can go from there to answer your question.
Yeah you could also use a set command (omron/ telemechanique) same as hold command, I think. You will also need to be able to reset the contactor using a reset command. How are you going to do this?
You may also need to create a interrupt function if the pulse is on for a short time.
If you are not using a plc the you could just do it with a normally open contact on your contactor, this will be more dependent on the speed of the pulse as contactors are a lot slower than PLC's which are inturn slower than industrial PC's
I m Not Using PLC, But is it possible to use a Latching relay between the Sensor and Contactor to hold the Contactor by single pulse of Sensor...... Please give feedback
But is it possible to use a Latching relay between the Sensor and Contactor to hold the Contactor by single pulse of Sensor...... Please give feedback.
Okay. Without knowing the brand and catalog number of your contactor, sensor, and relay, then here is a generic version with a generic pulse stretcher. With more information from you, I could give you more information in return.
Here are some pulse stretchers at this link. I do not know which one you need because it depends on the voltage of the circuit, the sensor, the relay, and so on. A retriggable monostable multivibrator is one type of electronic circuit that can be used as a pulse strectcher. You may not need the latching relay.
http://www.arcade-electronics.com/NTE_9675_p/nte-9675.htm
This version would be safer and preferred, unless your instructions specify the latching relay.
This circuit diagram will help give you an idea on how to construct a hard-wired Latch:
Then you definitely will need some electronic device that can "see" or read the milisecond-range pulse and convert it to a Start signal for a contactor. A pulse-stretcher is one such device. There are probably some solid-state relays that could react fast enough to turn on when triggered by a 10 milisecond pulse.
Yes, I see that the Opto Solid-State AC Relays will trigger or operate in 0.5 cycles, and some of the DC relays have a turn on time as short as 100 microseconds (0.1 miliseconds). At 60 cycles per second, 0.5 cycles is a 8.33 millisecond pulse required to operate the solid-state relay. Make sure that your pulse is 1.5 to 2 times longer than the minimum relay turn-on time. Then you would probably need a second electro-mechanical seal-in relay to seal in your contactor.
Okie, a solid-state timer is a brilliant solution. I wish I had thought of that!
The timer timed output (of 2 or 3 seconds duration) could be wired directly to the contactor, with a contacor seal-in contact to hold the contactor on until turned off by a stop button.
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
23
540
Hi everyone, I am working with micro850, a proximity sensor (FOTEK, PL-05P) and a 3DOF serial arm robot. I use MC_MoveRelative to control the...
108
Maybe a stretch to call this a PLC question, but it does connect to a PLC input. I have two German switches: Sick WL9LG-3P2232 And a...
124
Hi, Need help with coding for a faulty component sensor which we are using a push button as we are using a test rig. the plc is a allen bradley...
237
Hi all, I am implementing an incremental encoder sensor (ABZ) to replace the existing "manual" encoder wheel I have in my device. This is a 360...
184