I have a project where the PLC works in extreme atmospheres, such as -30ºC . Before install it the PLC has to been tested in a climate chamber at -40ºC. I can't find companies that supplies PLC to this conditions.
Which PLCs could be installed in such conditions?
Thanks for the answer
find companies with a marine approval like DNV, LLoyds, GL etc.
i use WAGO PLC (with Codesys) they do have approval, these low temps are not the biggest problem, the higher ones are.
operation is from -20 to +60
extended range is possible, however there will always be some heat by the PLC, so a little heating in an insulated box should be possible.
The biggest problem with low temps are the capacitors mounted, the rest is no big issue.
Another possibility is to make yourself a small board wit a mega328 very simple no external parts needed. see arduino for examples)
Have a look at the Twido Extreme from Schneider
http://www.global-download.schneider-electric.com/85257578007E5C8A/all/0359D15C740CCFEA88257577000C0742/$File/35013462_k01_000_05.pdf
from the manual
Environment Characteristics
The operating environmental characteristics are as follows:
Characteristic Description
Operating temperature range -40C to +110C (-40F to +230F)
-30 is normal tempereture here in winter time. Therefore we are heating houses, as well PLC-Cubicles. Inside The Cubicle we can use insulating material as polyurethane plate in door and walls.
Rittal have suitable heaters and thermostat that you can enable voltage for PLC etc. when temperature is enough warm inside. Remember humidity also.
Then after, you can use everything you like.
I'm don't have time to read the forum as much as I used to - so maybe I've missed anything posted about this subject ... I ran across it and...
1,568
Hi everyone! I am new to PLCs and need some help. I can brute force my way through the ladder logic, but the actual PLC installation & wiring...
1,579
Does anyone have any experience with QTERM HMIs by beijer electronics? I am looking for some kind of HMI that we could use in an outdoor...
1,897
Any one have experience with the rio function on the Mettler Toledo weigh scale General Purpose JAGExtreme Thanks
1,179
Hy guys, we need hmi’s for ambient temperature 65 ºC, high humidity, explosion proof, and connectable to Siemens plc s7-400. Siemens do not have...
1,977