I have a simple timing sequence ive been playing with, question is, i cant get my /DN bits to cause a transition for the CTU.
Am i missing something here?
Ive attached a screenshot. below
To elaborate a little, you are resetting C5:1 before you are trying to count C5:2.
Mickey's solution will work. If you are trying to use C5:1/DN in later rungs that we cannot see in the picture, then it might make sense to move the C5:1 RES above the C5:1 counter.
Ctu
harleymc100,
This is called ORDER OF EVALUATION
Means, where you place your rungs/networks , has great impact on your program behavior
Regards
Safe rule of thumb is that things read top down and left to right. There are some caveats, but you eliminate most problems if you arrange your program into steps that follow that rule.
.....For this reason you can't Jump to a label backwards, otherwise the CPU will fault.
Yes you CAN jump "backwards", but you MUST NOT do it indefinitely - there must be a way to terminate this jumping, or the watchdog will time out and fault the processor.
Now, one kinda dumb question that I have is that would OP's Logic work on a ControlLogix CPU? I know scan cycle is a bit different. Just curious.
No, the RES instructions would work exactly the same.
The only difference is that the physical IO scan is asynchronous, but updating if internal tags is not.
Hello, I have a flowmeter, it pulses once per gallon. I have my discrete input pulsing away along with the flowmeter. I can count the tenths...
2,793
309
I've got a Micrologix 1100 with ethernet and I'm trying to configure communications to a Fanuc R30iB controller. I'm pretty sure you have to set...
124
So here's my situation, I have been tasked with modifying the logic to mimic a button press in the PLC. I have two identical machines however one...
561
Hello, I'm new to programming. I'm using RSLogix500 to modify an existing program for a SLC500. My plan was to use one of the existing inputs...
26
2,055