TWINCAT V3 : timers in function block
dezuiper
Dec 2017
Belgium
I have just started programming in TWINCAT to get some experience in structured text. I have just finished my first function block but I have hit a problem. My timers do not count inside a function block. What am I doing wrong?
The block is manipulated via a visualization.
Code:
PROGRAM MAIN
VAR
    myValve : FB_PNUEMATICVALVE;
    setOpen : BOOL;
END_VAR
myValve(bSetOpen:=setOpen);
Code:
FUNCTION_BLOCK FB_PNUEMATICVALVE
VAR_INPUT
    bSetOpen : BOOL := FALSE;
END_VAR
VAR_OUTPUT
    uiWarning : UINT := 0; //b1: valve sensor error
    bIsOpen : BOOL := FALSE;
END_VAR
VAR
    fbTimerValve : TON;
    fbTimerFeedBack : TON;
    usiState : USINT := 0;
    usiLoopAttempts : USINT := 0;
    bSensorOpen : BOOL := FALSE;
    bSensorClosed : BOOL := TRUE;
    bValve : BOOL := FALSE;
    bFeedBack : BOOL := FALSE;
END_VAR
CASE usiState OF
    0: // STATIC
        IF bSetOpen <> bIsOpen THEN
            fbTimerValve(IN:=TRUE, PT:=T#100S);
            //fbTimerFeedBack(IN:=TRUE, PT:=T#50S);
            usiState := 10;
            bValve := bSetOpen;
        END_IF
    10: // MOVING
        IF fbTimerValve.Q THEN
            fbTimerValve(IN:=FALSE);
            IF bSensorOpen OR bSensorClosed THEN
                uiWarning := uiWarning OR E_BIT_MASKS.b1;
            ELSE
                uiWarning := uiWarning OR E_BIT_MASKS.b2;
            END_IF
            usiState := 20;
            RETURN;
        END_IF
        IF fbTimerFeedBack.Q THEN
            fbTimerFeedBack(IN:=FALSE);
            uiWarning := uiWarning OR E_BIT_MASKS.b5;
            usiState := 30;
            RETURN;
        END_IF;
        IF (bSensorClosed AND NOT bSetOpen) OR (bSensorOpen AND bSetOpen) THEN
            usiState := 0;
            bIsOpen := bValve;
        END_IF
        IF bFeedBack = bValve THEN
        END_IF
    20: //ERROR, try looping
    30: //Crititcal ERROR, do nothing
END_CASE
Is this the proper way to handle timers?
Code:
[B]fbTimerValve();
fbTimerFeedBack();[/B]
CASE usiState OF
    0: // STATIC
            usiState := 10;
            bValve := bSetOpen;
        END_IF
    10: // MOVING
            ELSE
            END_IF
            usiState := 20;
            RETURN;
        END_IF
            usiState := 30;
            RETURN;
        END_IF;
            usiState := 0;
            bIsOpen := bValve;
        END_IF
        END_IF
END_CASE
You have the calls to the timers on the outside of the Case statement, which is correct--they need to run every scan. The preset value can be specified in the call since it never changes. You shouldn't try to re-execute the timer inside the Case; instead just change the IN parameter to enable or disable the timer.
Code:
fbTimerValve(PT:=T#100S);
fbTimerFeedBack(PT:=T#50S);
CASE usiState OF
    0: // STATIC
            fbTimerValve.IN:=TRUE;
            fbTimerFeedBack.IN:=TRUE;
            usiState := 10;
            bValve := bSetOpen;
        END_IF
    10: // MOVING
            fbTimerValve.IN:=FALSE;
            ELSE
            END_IF
            usiState := 20;
            RETURN;
        END_IF
            fbTimerFeedBack.IN:=FALSE;
            usiState := 30;
            RETURN;
        END_IF;
            usiState := 0;
            bIsOpen := bValve;
        END_IF
        END_IF
END_CASE
I put TON in CASE statements like this..
Code:
Case Seq OF
    10:
    IF fbMyTimer.Q THEN //advance
        Seq := 20;
    END_IF;
    fbMyTimer(
              IN := <Your Condition> AND (Seq = 10),
              PT := T#2s
    20:
    //next step....
This keeps everything to do with the timer in one place.
Putting the (Seq = 10) clause in tidies up behind itself.
I also use ENUMs for the Sequencer rather than an INT type variable, but that doesn't change the functionality.
Pp
I am using twincat 3 to send some strings over TCP/IP. Where the server is a sensor and my PLC is the client. I noticed that the sensor didnt...
74
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
222
Hi! I am trying to run the 'SimpleSample' (https://infosys.beckhoff.com/content/1033/TF5100_TC3_NC_I/Resources/3438746891/.zip ) to understand the...
106
I am developing a library in twincat and one of the function uses IID_ITcVnAccess_TcVnPoint2_DINT and the definition of this type is defined in...
72
Sorry if this has been asked before, and apologies if this seems like a trivial issue, but I am new to Beckhoff and have been banging my head...
152