Panelview 900 problem Error 60
Jean-Philippe
Feb 2010
Montreal
Hi everybody, I'm new in this forum. I have a Panelview 900 without user manual. The problem: The screen starts to flick, and "Error 60" was displayed on the screen. The touchscreen was unresponsive. I cycled the power and they never restart. The red light (fault) always stays on and even when I push "RESET" on the back nothing happen. Can you help me?
Pages B-17 and B-18 in the manual shown in the link above have the answers to your questions.
Thank you guys for the hints. So "error 60" is "CPU could not execute code". Do you think that the system is corrupted? When I try to reboot-it, instead of the "Self-test startup page", I only see unreadable characters and the screen turn black.
All those symptoms are consistent with a failed terminal. "Failed", as in broken and probably unfixable.
And that's bad news. The application program cannot be retrieved if the operating system can't boot.
The PanelView 900 Standard hasn't been manufactured for 5 years or so. The PanelView 1000 Standard terminals are still being built brand new.
For most failed PanelView 900 terminals, I try to do a conversion to the newer PanelView Plus platform.
Thank you for your time. I will remove the Panelview of my system: I will install an Honeywell Experion Station with a graphic display to replace it. This system was from a closed plant in Texas. We bring back some equipments in Canada and we tried to use it here but... That's ok. (y)
Panelview 900 communicates with SLC 5/03 PLC. When I upload the program from the panel, some buttons have the address B3/306, B3/304 etc. However...
2,474
System comprising SLC 5/02 CPU. Panel View 900, 2711-T9A2. Ser E, Rev A, Frn 2.02. Fault: Panel view not transfering Command to move motors...
4,422
Greetings Everyone: I was having a problem with a PanelView 900 (Catalog # 2711T9C8) that I believe is not communicating with its associated SLC...
4,997
Hi All, I have a panelview 900 which just got back from repaired. I downloaded a program to the panelview 900. The screen of panelview did show...
8,476
Hi, I'm trying to figure out how to properly update the "icons" on my Panelview 900 (AB 2711-T9C9). I think maybe I'm having a fundamental...
1,023