I need to sense 3 phase 240 volts

Trainelectric

Member
Join Date
May 2017
Location
Strasburg PA
Posts
7
There has to be something out there, I just don't know what terms to use to search for it.

I need to sense whether or not 240 volt 3 phase power is present.

Does anyone have recommendations, schematics, suggestions, old threads on how to sense whether or not voltage is present?

The situation is this: Passenger train. Three of the cars each have their own generator. Train gets plugged in at night . Each car with a generator can be powered by: the land line, it's own generator, or the generator of the car next to it. I would like to use a plc to sort out which source of power is the priority, whether or not to send power out to the rest of the train, whether it's own generator is running.

I was thinking about using a phase relays, but there are situations where it will not activate,which would result in the plc trying to put two sources together.

There is just voltage, not current, so I don't think a current sensor would work in this application.

The actual control is easy. I just need some suggestions on how to sense whether or not potential exists on the power inputs.

I currently use relay logic, but there are some drawbacks to this.

Thanks
Steve
 
You could just use 240V coil ice cube relay. If you don't need to sense all three phases, just one relay between L1-L2 would suffice.
 
thought of that. the problem is that I could have two of the three phases (the plug between the cars loses one), the detector would not turn on, which would trick the plc into thinking there's no power there, so it would then try to hook two sources together, which results in a rather spectacular light show. Don't ask me how I know that.
 
If its that critical - double them up per phase, so 6 relays in total and read all 6 inputs.

The chances of 2 relays sticking closed is almost impossible.
 
We do something similar, not to detect phase presence, but phase loss. We do this with a current relay in each phase. Thus we get confirmation of the entire path, but then only when current is supposed to flow of course. The 3 relay outputs are connected in series and then to a single PLC input.
In your case you should connect the 3 relay outputs in parallel and then to a PLC input. It is enough to generate an alarm.
 
Another take.

If the various power sources are connected via plugs and there are lids on said plugs, then you can monitor the lids. Only one lid may be opened at a time.
 
I think that any system that is designed so that a PLC fault can cause fireworks probably needs rethinking. I would look at using changeover contactors so that two supplies can never be connected at the same time. Or at the very least mechanically interlocked contactors.
 

Similar Topics

I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
338
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
164
Good day all! Can someone help me with the procedure to update Beijers E700 firmware? The Panel I am working on is firmware 2.04v and I would...
Replies
1
Views
70
Good evening. I display the step number of a SFC on a display. Sometimes, on a trip, it goes quickly through many steps and I need to prove to...
Replies
1
Views
129
Good morning all. I'm working on a rehab where they had a standalone InTouch 2014 HMI that they called a SCADA, but it's really basic stuff. The...
Replies
4
Views
182
Back
Top Bottom