E/H Promass 100 Totalizer Reset on ethernet i/p

My understanding is that they have two ethernet ports one for configuration and the other one for EIP. The one for configuration i guess is the one to be used to handle totalizer reset.
From Endress manual: The address line of the Web browser, e.g. http://192.168.1.212/basic.html.
A fully functional but simplified version of the operating menu structure
starts in the Web browser.
 
Been a while but I seem to remember some "clear" type bit in the AOP structure you set.
 
On the promass 100 on ethernet ip. The totalizer is cleared by putting the totalizer control number from the config instances into the totalizer control in the output instance.

For my application it was 198.

So to clear it i moved 198 to output then moved 0 to it when it cleared.

The promass 83 i had used in past had a actual reset output.



.
 

Similar Topics

Dear All, Currently i'm working with Endress Hauser flowmeter and AB PLC and try to integrate with 2 items. Flow meter spec using is Promass...
Replies
3
Views
52
How is it going y'all? So We have had a pesky problem with an EH 300 flow meter. We are using EIP to reset the totalizer, and for some reason the...
Replies
3
Views
860
I have a project including S7-300 CPU 314 2PN/DP and this CPU will communicate with Promass 83DP. I tried to connect the flow meter through the...
Replies
4
Views
2,930
Hello All, we have several ethernet IP promass 83 flowmeters from Endress + Hauser in our facility that we use to measure how much material we...
Replies
13
Views
2,425
Does anyone have any insights on how to use these meters with Ethernet/IP? The values on the input table look fine, but I can't figure out how to...
Replies
7
Views
5,790
Back
Top Bottom