How to establish communication between SLc 5/03 and multiple Modbus devices

If any body have the solution of the following problem, please help me out.

The problem is that I have an SLC 5/03 PLC in the control room and four microcontroller based compressors situated in class I, Division 2. All of these microcontrollers have RS232 port with Modbus PTU protocol. (Two compressors are 'AMOT' make and other two are 'Selectronics' make). The distance of each compressors from control room are 160m, 140m, 180m and 80m. Please suggest;

1. which type of protection do I use on the signals going to the hazardous area i.e. isolators or safety barriers or some thing else and do I have to place it on both sides?

2. Do I have to put a DH485 to RS232 converter at each end of the microcontrollers and put them in daisy chain and connect it to the SLC 5/03.
Does it will work or do I have to adopt some other scheme?

3. Please, suggest that how can I connect two personnel computers (both are running Rsview 32) and two printers, to the above network.

Please guide me I any one had such experience and thanks in advance.

Hassan.
  Reply With Quote
Old August 7th, 2007, 02:03 PM   #2
Joe_WaZoo
Lifetime Supporting Member
United States

Joe_WaZoo is offline
 
Joe_WaZoo's Avatar
 
Join Date: Oct 2006
Location: Murphy, TX
Posts: 301
Hassan,

The DataStation Plus from Red Lion could allow you to talk to 3 of the Modbus RTU devices and also to the AB 5/03 via DH485 with the use of the expansion card. Or you could use the RS-485 port from the Red Lion unit to talk Modbus485 and then have a 485 to 232 converter at each microcontroller. And then use the Red Lion RS-232 port to talk DF1 to your SLC. The Red Lion DataStation Plus also has Ethernet port on it to talk Native Tags to RS_View 32. Here is a link to that on the web.

DataStation Plus

This product will allow you to get the Modbus info into the AB PLC world very easily.

I would reccomend the DSPLE model at the least.

Joe_WaZoo
__________________
TURCK Network I/O Guy, Banner Wireless knowledge, & Red Lion HMI stuff! Yes I am the techie geek for the local Rep Firm Automated Dynamics Corp covering the states of TX, OK, AR, LA, MS, part of TN, and a little bit of Mexico.
  Reply With Quote
Old August 7th, 2007, 09:07 PM   #3
Kim Gold
Member
Canada

Kim Gold is offline
 
Kim Gold's Avatar
 
Join Date: Jun 2002
Location: Stoney Creek, Ontario
Posts: 241
Another product you might want to look into is a ProSoft 3150-MCM module. It will fit into the SLC 5/03 rack and will allow you to talk to Modbus devices.

http://prosoft-technology.com/content/view/full/5757

Kim
  Reply With Quote
Old August 18th, 2007, 12:08 PM   #4
M. HASSAN
Member
Pakistan

M. HASSAN is offline
 
Join Date: Oct 2004
Location: KARACHI
Posts: 6
As I have mentioned that the distance between the SLC and the micro_controllers is around 600m. Please tell me, if I connect a cable from the Prosoft card to the micro_controllers and put them in daisy chain than does it will work or not. Secondly, should I use a 02 wire Cable based on Rs-485. Please, reply.

Last edited by M. HASSAN; August 18th, 2007 at 12:16 PM.
  Reply With Quote
Old August 18th, 2007, 01:05 PM   #5
Kim Gold
Member
Canada

Kim Gold is offline
 
Kim Gold's Avatar
 
Join Date: Jun 2002
Location: Stoney Creek, Ontario
Posts: 241
The longest installation we have using a Prosoft card is approx. 300'. We are connecting to 3 Multilin 469's in series. We are using RS485 at 9600 baud.
We are using the recommended cable which is Beldon #9841.

The maximum length of RS485 is listed as 4000 ft or 1200 meters.
I believe the max. length of RS232 is listed as 50 feet although we have found it will generally works even at longer lengths.

I would not think RS232 will work at a distance of 600 metres. I would think you may need a convertor.

Kim

Last edited by Kim Gold; August 18th, 2007 at 01:08 PM.
  Reply With Quote
Old August 25th, 2007, 12:40 AM   #6
M. HASSAN
Member
Pakistan

M. HASSAN is offline
 
Join Date: Oct 2004
Location: KARACHI
Posts: 6
Thanks a lot for your replies. Mr. KIM you are right, we have to place a repeater for long distance communication (600m in our case)via prosoft card. Can you please tell me, if I have to place a safety barrier or Isolator at both ends, because I have to establish a communication link from control room to compressor's (04 in nos.) located in a hazardous area, class I, division 2.
  Reply With Quote
Old August 25th, 2007, 04:14 PM   #7
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,763
1) EIA spec for RS-232 is short distance, somewhere on the order of 15 or 20 meters. The distances in this application definitely require RS-485. RS-485 can go to 1,000m distances. Use shielded comm cable that includes a wire for a ground.

RS-485 should not need a repeater, but if you need use an RS-232 port on something like a Prosoft card, then you need an RS-232-RS485 converter.

2) An RS-232-485 converters can be rated for Class 1, Div 2 hazardous areas.

For example:
http://www.bb-elec.com/product_multi...ltiFamilyId=59

Models like these also provide isolation, which is very important for protecting the relatively expensive RS-232 ports on the drives and whatever Modbus module you use on the SLC.

I always recommend isolators even when hazardous areas aren't an issue to protect the hardware ports.

3) Mr. Yazoo's comments on the RedLion DS+ as a converter between Modbus RTU and DH+ seems to work for others.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Beijers E1000 - Modbus Multiple Write Command Philg LIVE PLC Questions And Answers 3 September 30th, 2010 12:18 AM
AB-Communication of multiple devices unsunghippie LIVE PLC Questions And Answers 1 March 29th, 2007 10:06 AM


All times are GMT -5. The time now is 09:39 PM.


.