hello ,
i have a devicenet network that includes 2 Powerflex 70 and 4 SMC Flex ,1 panelview plus & Controllogix.
Powerfelx control mode is set for 2 wire Control.(only digital IN 2 as Start)
I'm interested to send start /Stop command and Frequency Ref from the Controllogix by using Logic Cmd Word .
According to this publication page 141 (
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/20comm-um002_-en-p.pdf)
this is impossible with the current configuration.
Do you know any workaround for this issue?we need to have a local/remote control like this:
Local;start/stop from input 2;Frequency command:from HMI
Remote: start/stop &frequency command from PLC
thanks in advance for your time ;