Purged panel & pushbuttons
cornbread
Feb 2007
madison, indiana
407
A bit off topic, but I'm sure this esteemed thread will have some answers. I'm having a debate with our engimneering group on what push buttons to use on a purged panel in a class 1 div 2 area. The purge I think is a Z purge (alarm only). I contend a stanadard pushbutton is OK, engineering says I have to use explosion proof. What say you?
From a purely technical viewpoint, you are both wrong. If engineering says "explosion proof" is required, no, the most severe case would be pushbuttons rated for Class 1 Division 2, not "explosion-proof" (whatever that means). Note that many pushbuttons that you may call "standard" (whatever that means) such as the Square D Class 9001 Type K, SK, or KX are qualified to be used in a Class 1 Division 2 area.
If I will be working in the area, then I would use pushbuttons that have a Class 1 Division 2 rating. One the other hand, if the engineering guys are going to be the only ones working out there around the purged panel, then I would just use any old switch off the shelf. :ROFLMAO:
The definition of a Type Z purge makes a Class 1 Div. 2 area non-hazardous. So if it's realy a type Z purge, so should be able to use standard pushbuttons in the panel.
I can buy a standard pushbutton at Walmart for a doorbell button, but I don't think that would work too well. "Standard" doesn't mean anything. Standard for what, whom, and where? The best bet is to specify a brand and type, then you know something about the pushbuttons.
If you work in one plant that uses only one type of button, then maybe you can call it a plant standard. But that standard button might be rejected by another plant next door - it could use a completely different "standard" pushbutton.
I suppose this comes from working for a contractor in too many different plants with too many different standards that each one thinks is the cat's meow.
Lancie, did not you were such a big fan of engineers!!
Bruce, I were one, after being a farm hand, a busboy, a sewing machine mechanic, electrician, and a few other things for short periods (logger, heavy equipment operator, technical writer), so should be allowed to poke fun at that group "as a hole".
Hi guys Need help in setting up Wireless router for Zone0 , inside a Purged unit, communication 200m, using PLC Siemens anyhelp would be much...
1,527
Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
80
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
204
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
396
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
84