Hello, I have a curious problem of mismatch between RSLINX and Logix Designer regarding the major revision of a device.
Gear:
*Logix Designer V32
*1756-L84E (V32.14)
*Stratix 5700 1783-BMS10CGP (V12.004)
When I'm connecting to the Stratix with RSLinx Classic, I get all informations as usual.
But when trying to add the Stratix as a Ethernet Module on my PLC config, the choice of major revision doesn't go up to 12 (maximum being 10).
I tried uploading the EDS from device (RSLinx). But Logix Designer won't update the EDS to match the major revision V12.
Any clue anyone ? Thanks in advance!
I think you need to download and install the latest Stratix Add-On-Profile from Rockwell to get firmware rev 12 to show up.
Thanks benaiahhenry,
it was exactly it : I downloaded and installed the Stratix AOP (latest) from Rockwell and then it worked.
Problem solved, Thank you
Lately, me and my coworker run into issues with opening some 5000 files. With some V19 files, the splash screen pops up then.. nothing. This...
4,059
Hi, I came across a thread somewhere mentioned that, we need a new activation key if there is an upgrade in the major revision of the software...
9,949
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
112
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
1,122
Hi Guys Today we went through the worst situation that PLC went to major fault Mode due to Trap by one of the Timer with -ve Value Moved into...
1,043